Do I have enough outlets?


estesbubba

Recommended Posts

Final thought -- figure where your flat screen will reside. Wire the string of T5s/T8s in front of the flat screen on a separate wall switch. This comes in handy when you declare a 'sharpening afternoon' and just want to watch the game while sharpening... Eliminating the glare from that first string of lighting goes a long way to improve your shop's multi-media viewing...

 

BTW: safety tip: orient the screen so that it's at your back for the majority of power tool operations... You don't want to be distracted by Cheerleaders while ripping stock.. :) There's a wood joke in here somewhere, but I'll pass...

Link to comment
Share on other sites

  • 3 weeks later...

Estesbubba,

 

Lots of good advice here.  One thing I would add would be GFCI receptacles.  Most equipment works just fine, some may false trip the device so you may have to remove it.  12 gauge / 20 amp circuits are preferred and keep your lighting separate from your power.  Keep the runs as short as possible and if extension cords are used make sure they also are 12 gauge.  The number of circuits is a function of how much will be running at the same time, not the number of receptacles on the line.  Think total possible load and go to 80%.  Don't run circuits with excessive amperage.  If the nameplate rating of a tool is over 20 amps use a dedicated circuit for that tool.  The motor will have a running load and a locked rotor load, that can be 6 times higher.  Don’t size to the LRA.

As others have said it is easier now than latter so put in all you can dream of.  Running several runs of conduit is better than over sizing a run.  The more wires in a pipe the more you have to derate the ampacity.   When running pipe you can share the neutral, just remember to tie the breakers together.  Nothing hurts worse than getting between a loaded neutral and ground!!   Take it from a recovering master electrician

Link to comment
Share on other sites

All 120 circuits have GFCI as the first outlet as code requires it. Everything downstream from it are standard which are still protected. All 120 circuits are 20 amp and the ones next to each other are on separate circuits. Every wall has at least 2 120 circuits and at least 1 240 circuit. I still plan on adding a few ceiling outlets for the big machinery. I also have lights on 2 20 amp circuits. Here are some pics of how the walls are configured.

 

IMG_0166.JPG

 

IMG_0167.JPG

 

IMG_0169.JPG

Link to comment
Share on other sites

If the GFCI gives you trouble you are allowed a single non GFCI receptacle that is dedicated to the equipment.  Remember, that is single, not the duplex receptacles we typically use.

 

The shop is looking great!!!

 

Well most outlets will probably be used for equipment. So if it does give me trouble and I replace it with a single non GFCI, what am I supposed to do with the outlets on the load side?

 

Of course I hope I never have to worry about this and the GFCI behaves!

Link to comment
Share on other sites

You have what would be called an accessory building.  There are only 8 places where GFCI protection is required.  2014 NEC 210.8 (B) Other than dwelling units.

  1. Bathrooms
  2. Rooftops
  3. Kitchens
  4. Outdoors
  5. Sinks (within 6 feet)
  6. Indoor wet locations
  7. Locker rooms with showering facilities
  8. Garage service bays

You are putting in GFCI receptacles for your own peace of mind, not code.

Link to comment
Share on other sites

I think local code requires GFCI for detached buildings, but even if it doesn't, I'm at least meeting code.

 

So I didn't see a need for any 220 30 amp sockets. I don't have a welder in my future and don't see any WW machines down the road that would need over 20 amps. I guess if it does happen I can always run conduit or swim through the attic insulation. My Grizzly cyclone will require a 40 amp. 

Link to comment
Share on other sites

Is any of your equipment convertible to 240 V?  Some larger motors have the ability to be wired for 240V, I would take that option if it were available.  It was mentioned earlier in this thread to balance the load.  Tough to do in a one man shop with p\primarily 120V circuits but putting the heavy loads on 240V will do that, lessen the amperage per leg and reduce voltage drop during start up as well.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Who's Online   2 Members, 0 Anonymous, 43 Guests (See full list)

  • Forum Statistics

    31.2k
    Total Topics
    422k
    Total Posts
  • Member Statistics

    23,771
    Total Members
    3,644
    Most Online
    Kaiweets Tool
    Newest Member
    Kaiweets Tool
    Joined