woodtinkerer Posted December 21, 2011 Report Posted December 21, 2011 Hello all, I am looking to purchase a new table saw and i am leaning towards a grizzly, model #G0715P. I have a concern with it, it is said to be prewired to 220v, which of course i dont have in my shop. The instruction manual shows the conversion to be pretty simple, just removing a jumper and putting a second one in. But it specifies the plug on the end of the power cord will need to be changed as well and a new one can be picked up at any hardware store. It says to install a standard 5-20 plug on the end of the power cord. It looks like from the picture that it just has one of the blades horizontal. Does anyone know if this is required or can i use a standard plug type rated at 20a? If not does the wiring on the outlet in the wall change when i use the new style outlet? Thanks in advance. Quote
JayWC Posted December 21, 2011 Report Posted December 21, 2011 You always want the weakest point of the circuit to be the circuit breaker or fuse...not the device (outlet, switch, etc), wires in the wall or plug. The plug on the end probably needs to be changed from a 220V prong set-up to a 110V style plug. That's mostly so you don't accidentally plug it into the wrong voltage after it's all said and done. If you change the cord end to a 20A plug, you should also make sure your outlet is 20A. Your wires should also be sized for the amps and distance from the panel. You don't want the wires heating up in the wall and starting a fire or the receptacle melting and shorting out. Quote
Eric. Posted December 21, 2011 Report Posted December 21, 2011 You may as well just run a 220 line out to the shop. Your TS will thank you. Quote
woodtinkerer Posted December 21, 2011 Author Report Posted December 21, 2011 thanks for the quick reply. my question was more on the type of plug and outlet, right now the outlet in my shop has both blades of the plug vertical where as the manual has one vertical and one horizontal. Does that type of thing matter, just as long as i use the same plug and outlet type? And if it does does the wiring locations, such as which terminal on the outlet gets which wire, ie. white wire, black wire, change on the outlet? Quote
woodtinkerer Posted December 21, 2011 Author Report Posted December 21, 2011 You may as well just run a 220 line out to the shop. Your TS will thank you. that was my first idea but i hated to spend $900 on the TS and then god know how much to have a electritian come out to run the 220. Quote
TheWoodLab Posted December 21, 2011 Report Posted December 21, 2011 While I'm not 100% sure, if your outlet only has vertical slots, I think it may be only rated at 15A. The outlets I've seen that are rated at 20A should have a "T" like slot on one side (to accept both vertical and horizontal prongs). Remember that if you cut the volts in half, you are doubling the amperage needed - in which case you will definitely need a 20A circuit. Would that mean a new run you need to install anyway? That said, I also have the 715P and love it (running on 220v). Quote
dwacker Posted December 21, 2011 Report Posted December 21, 2011 You dont need any special plugs to run 20A @110vac. Your regular outlets if rated at 20A will work just fine. Lop the end off the cord and change the end. Rewire the motor and install the required circuit breaker for the saw if needed. Some of those little motors need a special breaker at the saw. Check to see if your outlet is on a 20A panel breaker if you question the wiring then remove the cover and make sure its big enough. The only difference is that the saw will no longer meet CSA / UL standards for home shop use which is the only certification it has anyways. Don Quote
Eric. Posted December 21, 2011 Report Posted December 21, 2011 While I'm not 100% sure, if your outlet only has vertical slots, I think it may be only rated at 15A. The outlets I've seen that are rated at 20A should have a "T" like slot on one side (to accept both vertical and horizontal prongs). They do make 20A standard three-prong 110V plugs and outlets, but they need to be run on 12ga wire and 20A breakers. That's what I have in my shop, and 220V on two other circuits. that was my first idea but i hated to spend $900 on the TS and then god know how much to have a electritian come out to run the 220. Shouldn't cost that much. Run some 12-2 from the panel to the shop, get a couple 20A breakers from HD that fit your panel, then call the electrician and have him wire your breakers and outlet if you don't think you can do it yourself. Shouldn't be more than a couple hundred I wouldn't think. If you're planning to go with bigger tools in the future, now would be a good time to do it since you got your new TS. It's easier on your equipment on 220V, too. Quote
dwacker Posted December 21, 2011 Report Posted December 21, 2011 Shouldn't cost that much. Run some 12-2 from the panel to the shop, get a couple 20A breakers from HD that fit your panel, then call the electrician and have him wire your breakers and outlet if you don't think you can do it yourself. Shouldn't be more than a couple hundred I wouldn't think. If you're planning to go with bigger tools in the future, now would be a good time to do it since you got your new TS. It's easier on your equipment on 220V, too. Careful that may not be accurate for the setup. My shop has 4 runs of #3 and that is bare minimum to meet code. Don Quote
Eric. Posted December 21, 2011 Report Posted December 21, 2011 Careful that may not be accurate for the setup. My shop has 4 runs of #3 and that is bare minimum to meet code. Don #3? Quote
dwacker Posted December 21, 2011 Report Posted December 21, 2011 #3? #3 copper HHNG from main panel to shop sub panel. Minimum to meet code 30a to 100a. Over 100A needs #2 copper. #12 is used for short runs from the panel to the outlet 20A and under, #10 for 30a. We have no clue how far the OP run needs to be so cant speculate on wire size. Don Quote
Eric. Posted December 22, 2011 Report Posted December 22, 2011 #3 copper HHNG from main panel to shop sub panel. Minimum to meet code 30a to 100a. Over 100A needs #2 copper. #12 is used for short runs from the panel to the outlet 20A and under, #10 for 30a. We have no clue how far the OP run needs to be so cant speculate on wire size. Don Gotcha. Yeah, to the subpanel, 12 gauge is no good. I was assuming he has a couple breaker slots open on his main panel and he could run it right off of that to the shop. His TS is only 2HP...surely 12 gauge on a 220V circuit would be sufficient, as long as his runs aren't too long, like you said. My two 220 runs are about 25 ft or so, and my electrician buddy told me 10 gauge was probably overkill, but I used it anyway. They're on 20A breakers, though. What size breakers do you have in your shop, Don? Quote
woodtinkerer Posted December 22, 2011 Author Report Posted December 22, 2011 thank you all for the info. I am not sure on all the terminology, but what i have is my shop is basically a detatched two car garage. I have an attatched to car garage on the house. So the attached two car garage has a breaker panel in it running everything in the garage, (which is just a few outlets, a few lights, and two door openers). I beleive it has its own panel because it was added on later. But anyway, the attached garage has its own panel which i believe is split off the main panel in the house. So when i built the detatched garage(my shop) i ran buried cable of 8-3 with ground, which is what the cable says, from a 30a breaker in the panel in the attached garage to the panel in the detatched garage. For the outlets in the shop i ran 12-3 gauge wire. Does any of this help? I had helped my father in-law a few years ago install a 220 circuit for a dryer in the house but i dont really remember what we had to do in the breaker panel. Is it just as easy as putting in a 220v circuit in my panel in the shop? and of course swapping out the outlet. Quote
Eric. Posted December 22, 2011 Report Posted December 22, 2011 I'm confused...do you have a sub-panel in your shop, or just the attached garage? If you don't, you'll have to run an additional circuit out to the shop for the 220, either from the main panel in the house or the sub-panel in the attached garage (if it has the capacity to support it). 220 is wired differently in the panel than 110 (I think...mine is anyway), so they have to be separate circuits. If you DO have a sub-panel in your shop (big enough to support an additional 220 circuit), then you can add the 220 breakers and run another line straight from there. I'm not an electrician, so my knowledge is rudimentary...wish I could explain it better. But no, you can't just swap out the breakers in the panel...two different animals...I think. Quote
woodtinkerer Posted December 22, 2011 Author Report Posted December 22, 2011 thanks for the quick reply eric, what i have is i have a panel in my detached garage, it is run off of the panel in the attached garage, and that panel is run off the main panel in the house. How do i know if any of the panels (or more specifcally the one in the detached garage) can support the 220? Quote
Beechwood Chip Posted December 22, 2011 Report Posted December 22, 2011 If the breaker for the sub-panel (in the main panel) is a double breaker, in two slots, then it is a 220V breaker and you've got 220 on the sub-panel. At least, that's my understanding. Quote
woodtinkerer Posted December 22, 2011 Author Report Posted December 22, 2011 If the breaker for the sub-panel (in the main panel) is a double breaker, in two slots, then it is a 220V breaker and you've got 220 on the sub-panel. At least, that's my understanding. I know the breaker for the detached garage is a double wide, (it is taking up two spots). Its twice as wide as the rest and its a 30a. is that what you mean? Quote
Eric. Posted December 22, 2011 Report Posted December 22, 2011 It's beyond my expertise, and I don't want to give you bad advice. A friend of mine is an electrician...he just told me what wires to run and where, and he did all the connections and panel work. So basically, I'm not sure. Maybe an electrical forum would be a good place to ask...I'm sure they exist. Quote
woodtinkerer Posted December 22, 2011 Author Report Posted December 22, 2011 well kinda sounds like i should just look for a different saw. Thanks for all the info. Quote
dwacker Posted December 22, 2011 Report Posted December 22, 2011 well kinda sounds like i should just look for a different saw. Thanks for all the info. No the saw is fine the issues are the same no matter what saw you choose. You have a 30A @220v going to your shop that is just small for a shop. If you have two open slots in your shops panel you could just run a 220v 20a outlet. It wont matter if you run the saw on 220v or 110v you are loosing the benefit of 220v with your wiring. If your shop is wired properly your lights are on one leg of the 220 and the outlets on another leg. If you wire it 220 one leg will be shared with the lights and at 30a your pushing it depending on your lighting. If you wire it 110 as long as nothing else is running you will have a dedicated leg. The issue I see is dust collection. You dont have enough to run the saw, lights and a dust collector without maxing out the 30A. So basically wire it up 110V is probably the easiest. Wire it up 220V then it will most likely dim the lights when started. This means you have a weak leg and is actually harder on the motor and defeats the purpose. 110V imo is the best option short of running a new 50 to 100A service to the shop. Keep in mind you can convert it back to 220 later if you decide to install a bigger shop service. Don Quote