220v power tools on dryer outlet? (and other 220v questions)

Featured Replies

I have to admit that when it comes to electrical stuff, I am a bit of a dummy. Wired and assembled plenty of computers, but never messed much with how power tools operate out of the box, always running everything I have on 110v outlets.

Anyway, I'm clearing the second room of my basement and depending on how that goes, I 'may' have additional room for a jointer in the future. I'm pondering getting an 8" jointer, but the one(s) I'm eyeing runs on 220v.

The only 220v in my basement is the dryer outlet. I've done some hunting on the web on plugging power tools into dryer outlets, but I've got scattered information on the subject, some recommending not to do it, while others seem to have done it fine. Is a dryer outlet suitable to plug 220v power tools into, or is there a safety risk? (If there is, my decision will be made for me, I can go no higher than a 6" jointer.)

By the way, bringing electricians over to alter/add outlets isn't an option, I'm a renter.

Assuming that it can be done, I have a second question, involving converting a table saw to 220v. Different woodworkers/store clerks/etc have said that converting a table saw to 220v is dead easy. I understand changing the configuration of the wires in the saw (instructions on this in the manual), but information is far more vague on the power cord itself.

Am I just cutting off the end of the cord and replacing it with a 220v plug (one that would match my dryer outlet)? Would soldering of the wires be required for this?

Am I just cutting off the end of the cord and replacing it with a 220v plug (one that would match my dryer outlet)? Would soldering of the wires be required for this?

Changing the cord / plug to match the tool to the dryer plug is not difficult, but it's important for it to be done correctly. Solder is not normally used, these types of things usually connect with lugs and screws. A typical dryer circuit has more capacity than needed for most power tools, so you should be good to go.

Most 220v tools sold in the USA do not come with power cords. It's up to the user to purchase a suitable cable and plug, as well as install it.

If you're unsure, hire a local electrician to make up and install a cord on each tool that fits your outlet. This is not rocket science, but the price of failure is high.

You can, as a renter, have a licensed electrician come over to install 220 line. The catch is that you are getting it installed as a second 220 line, or a replacement dryer line for piece of mind. It's always a good idea to let your landlord know about it first, though. And there's no need to state what the 220 line is for; most will assume it's for a second dryer. (there have been several times i've wanted a second dryer anyway.)

If you have them come over to install a replacement line, that's usually something that can be reimbursed and does not always need permission. Especially if you are upgrading to cable that is in code from something that is not.

But this is always dependent on the location you are renting from. I was in a house once where the landlord was cool with just about anything we did. The place before that, we weren't even allowed to change the shade of white paint they used to paint the walls.

  • Author

Lugs and screws to put on the plug makes sense, just was trying to picture the process in my head. Have a network engineer friend who also does electrical work, might get his help. At any rate, don't need to worry about it right 'now' anyway. Thanks for all the advice.

You can use your dryer outlet just fine there is nothing special about it. Run to the panel and see how big of breaker it has prior to buying your 220v jointer. I think once you get the to cord end in your hand you wont have any problems at all. Installing a cord end is pretty self explanatory. Converting the saw is also very traight forward. Post some pics and we can easily step you through it.

Don

  • 3 months later...
  • Author

I'm revisiting this thread because it has become relevant again due to current events. First off, I took a plug apart and see the lugs and screws, so I'm clear on what needs to be done there. But I have a dilemma.

As I said in another thread here, I just purchased a Powermatic model 60 8" jointer, which can be wired to either 110v or 220v. The manual I found doesn't say anything about how many amps it draws, but as it had already been suggested here, I can't imagine it drawing any more than 15a.

Anyway, it didn't occur to me to ask them what it had already been wired at, and it turns out it's wired at 220v: an orange cord with this kind of plug: http://media.photobu...rr/3a923e9b.jpg

My dryer port I mentioned is also three prong, but it's this kind of port - a 115/250v 30a port - which is common on older houses from what I understand: http://applianceguru...ryer_outlet.jpg

So I have two options: convert the machine to 110v or leave it alone and get a 220v cord with an appropriate plug. Once again, the manual said nothing on how to do so / what cords to change (unlike my table saw manual, which looked straight forward). I opened up the box on the motor hoping for a diagram, nothing but wires joined together with wire connectors and electrical tape.

Figuring it was smarter to leave well enough alone and life would be easier if I just left it at 220v, I put everything back and ventured out to find a plug, as well as an appropriate 10-3 cord - about 8-10 feet in length - as I have no clue what gauge the current one is.

Went to the BORGs, although they sold many kind of dryer plugs, the only one they DIDN'T have was mine. Each time, the clerk brought me right over to the 10-3 dryer cords like these: http://www.partsread...302305wire4.jpg , saying that no one sold the plugs alone due to safety reasons (which doesn't explain the other types of three prong dryer ports which had plugs available).

So making my own cord was out of the question, and I might have walked off with those dryer cords...except that 6 feet isn't going to cut it. The jointer will be located next to the washer / dryer (my shop is shared space) and I need something long enough to reach the port. Since the cord would be hooked to the power switch on the inside and run through to the back of the machine, I'm already giving up length there alone. Eight feet 'might' do it, I would feel more comfortable with 10.

But alas, the BORGs don't sell anything longer...'safety' issues once again. Which I understand all of the above to prevent some bozo from wiring a 100ft extension cord, but we really can't go just a few more feet on these cords?

So I'm not sure what to do here...what are my options to get running? Is there a way to get an appropriate length 220v cord with my plug that will work...like wood, perhaps I shouldn't be looking at the BORGs? Or am I better off rewiring the unit for 110v? (Which I'm highly likely going to have to have a professional do, unless clearer directions / wiring diagrams can be found)

The plug on your Powermatic is a standard 220V-20A plug; it would be 15A if both prongs were horizontal. The cord only needs to be 12A if you're going a reasonable (<25ft) length.

That older dryer port isn't so much deprecated because it's unsafe as it is not needed anymore. Old dryers (long ago) used the 110V circuit to run mechanical timers and 220V for the motor and elements. For a long time now, dryers use solid-state timers that run on 5VDC; they include a step-down, the equivalent to those lovely wall warts for computer accessories.

The modern socket has just 220V. You only need 220V anyway. You could (or you could hire someone) add a NEMA 6-20R receptacle in a surface-mounted box near your dryer outlet and hook it in parallel. Since you said before you were renting, you could easily remove the surface-mounted box, plug the 3/4" hole in the drywall, and remove the wires when you move (or leave the hole since you lost you deposit already anyway! :)

A modern equivalent to the older dryer outlet is a generator outlet as it presents two hots, a neutral, and ground. This is what I wired for my SawStop so a single 12Ga cord coming off the wall goes to the saw and powers the saw (220V), router (110V) and an overhead light (110V) without a mess of cords. In your other thread, I put the link to my article on the router table and it includes links to this wiring. Reading that you'll get more insight to on the sockets you're looking at.

  • Author

By the way Paul, love the Festool videos ;)

About having a 6-20R receptacle wired, I'm worried the electrician will simply say 'not without the landlord's permission,' and I think things would just be easier for our relationship if the landlord never knows I have a woodshop downstairs ;) Asking the electrician to install a cord or rewire my unit for 110v might be easier since it's my machine.

Speaking of which, the plot thickens. While I was investigating the motor, I had snapped a photo of the wiring inside for reference. Later I was assembling the mobile base and prepping the flange when I happened to look inside and noticed something on top of the motor's junction box. Since it was at a weird angle, I moved in with my phone and it appears to be a wiring diagram.

jointer.jpg

The only thing that threw me at first was that I had expected a R-W-B-etc color guide, but upon inspection of the wire photo, looks like those wires are numbered and the ones I can make out match up to the high voltage diagram so far. I'll have to get back in there and take a better look, but that low voltage diagram may be what I need to go 110v? If so, the cord would be a cinch and wouldn't have to worry about the dryer plug nonsense.

Well, excellent, and it even lets you wire it to run the motor backwards; will it put stuff back on the wood?! :)

That's an easy change. One problem you may encounter is that the motor wired for 110V might pop the breaker on startup due to the startup surge. It's less on a jointer than a bandsaw; my bandsaw wired for 110V, I swear, popped it more often than it started until I switched to 220V (previous bandsaw; LT-18 is only 220V). If you're sharing that circuit with lights n such, it may be more of a possibility. Just an FYI.

The dryer socket idea would be pretty easy for you to tackle. A $4 voltmeter from Harbor Freight will even help you verify you got it right (and it's kinda hard to get it wrong: green goes in one place then connect reds everywhere else!).

Thanks, too, for the compliment :)

I've always wondered how to do something like this. When we emigrated from England, I brought a lot of 220v power tools with me. I ended up buying a transformer to step up to 220v. Since moving here, I've been wondering how hard it would be to take a 220v socket (seeing as you have them) and being able to plug my 220v tools into it. I suspect the easiest and safest thing would be to get a dryer plug and wire it into a power outlet I brought with me from the UK

All of the tools I brought with me have worked just fine on the transformer. There's a voltage selector, but no frequency selector on the transformer. None of the tools have caught fire, and I don't expect them to live as long as they might have done in England. I'll check the tools out and see what they say.

If it's not a 50/60 capable tool, a 50 Hz tool may still work fine in the USA.

I've read that 50 Hz (Euro) tools work fine on 60 Hz (US / Canada), but not the other way around. I have personal experience with my wife's USA spec hair dryers performing poorly and overheating when we travel to the UK and Europe, but haven't had experience with Euro spec motors in the US, only book knowledge.

All of the devices I've bought in the last few years were capable of running on either frequency.

I've always wondered how to do something like this. When we emigrated from England, I brought a lot of 220v power tools with me. I ended up buying a transformer to step up to 220v. Since moving here, I've been wondering how hard it would be to take a 220v socket (seeing as you have them) and being able to plug my 220v tools into it. I suspect the easiest and safest thing would be to get a dryer plug and wire it into a power outlet I brought with me from the UK

Your home's service panel is 220V; 110V is created locally by introducing a neutral line bonded to ground (a simplification; some situations require something else). If you own the house, you should have little problem loading up your shop with 220V; easiest way is a subpanel.

You'll have a lot more convenience than having to lug a step-up transformer around. Since you said step-up transformer not power-converter, you're still running on our cycles. There's no phase to be concerned about since it's single phase. As a note, within reason, universal motors don't care about the cycles that's why they are called universal motors. The difference in cycles will affect the speed slightly.

Only problem you might find is locating sockets that match the tools' plugs; worse case, buy new pigtails and put them in your tools; keep the old ones for whenever you want to resell them.

I recently and successfully installed two 220 lines (30a and 15a) without any issues, but only after a lot of online research. It's actually fairly easy once you understand all the inherent and not so inherent dangers of doing it yourself. Making a mistake here affords few if any second chances.

In any event, Paul's advice throughout has been spot on from my understanding. Just do your homework before attempting to tackle 220 lines. There's no such thing as being overly prepared or cautious in this arena. The safest route is to pay an electrician to do it for you. Your life is worth more than anything you might have saved doing it yourself.

Pulling the cable is a time consuming and pretty straightforward task. I have an electrician who will come by to talk over the job with me, then he'll go away and I'll pull the cable, run the conduit, etc, and then he'll come back and do the connections and check everything over. That way I'm not paying him electrician rates to do menial work. As I've grown more comfortable, I've started do more of the connections myself, with him checking it over afterwards.

He doesn't mind working small jobs evenings or weekends, which is great for a DIYer like me. He gets the little jobs that the "big" electricians don't like. You may not be able to find an electrician like that, but it doesn't hurt to ask around.

  • Author

I was referred to a site and tracked down a lone head for a 10-30 plug, unfortunately gotta wait for that to ship. But I was curious...if it's just a matter of changing the head and the black / white / green wires are the same on both, couldn't you technically do something kind of like the following link, making a conversion extension cord of sorts with the 6' 10-30 dryer cord as the cord and the 6-20 (or whatever the saw/jointer/etc needs) as the female on the other end?

http://www.hobartwel...=1&d=12045896

Nevermind, turns out Lowes had the plug I need after all!

Other things to do: check out the smaller (and older) mom'n'pop hardware stores. There's one I used to go to regularly (moved out of the area) that still has some stock on their shelves from when they opened. (In the early 1900s....) While spec's may have changed since then, they may know of people who have the current (no pun intended) plugs or sockets necessary. Plus, if you can find one where the prices are reasonable, you can find some of those smaller electricians dropping by. (At least go for the free coffee most offer...)

  • Author

Other things to do: check out the smaller (and older) mom'n'pop hardware stores. There's one I used to go to regularly (moved out of the area) that still has some stock on their shelves from when they opened. (In the early 1900s....) While spec's may have changed since then, they may know of people who have the current (no pun intended) plugs or sockets necessary. Plus, if you can find one where the prices are reasonable, you can find some of those smaller electricians dropping by. (At least go for the free coffee most offer...)

Ah, those are the best. Used to be a local mom n' pop in town (since the 40s) and despite being a small store, they ALWAYS had what you needed when the guys at the BORGs gave you the 'deer in headlights' stare and didn't have it (so much for having a large store). This place survived the onslaught of the BORG's fine, but the local college wanted the property and the hardware's lawyers couldn't possibly compete against their lawyers, so the hardware store had to abandon ship and move two towns over. I fell back to a Westlake ACE Hardware which was a decent replacement and had better quality screws/bolts/etc, but last week they closed their store leaving the BORGs the only places in town. I'm thinking I'll now drive two towns over to the mom n' pop just to snub the BORGs.

I mentioned this in another thread, but just in case someone is googling for this information and comes across it, Lowes / Home Depot is full of it if they say the NEMA 10-30 plug is not sold as it's out of code, etc. Look for a 10-50 plug instead, it comes with an extra "L" prong that can be swapped in to convert it to 10-30. Although it's kinda chintzy, I had ordered a 10-30 plug from McMaster-Carr (prior to discovering BORGs had them) and just got it, daaaamnnn what a nice plug. Very heavy duty.

As far as my adventures in 220v, turns out my best friend knows about this stuff. I showed him the wiring diagram and plugs, and he never gave a "Ummm..." or anything, understood instantly what I had to do and what needs to be done. I think I understand everything now, but he'll be checking my work to be on the safe side.

Just an FYI post:

My dryer port I mentioned is also three prong, but it's this kind of port - a 115/250v 30a port - which is common on older houses from what I understand: http://applianceguru...ryer_outlet.jpg

That is an older style of dryer receptacle officially called a NEMA 10-30R. These were used from WW2 up until the 1996 electrical code when they were replaced with the safer four-prong 14-30R receptacles. The same thing happened with electric ranges, just the 50A version 10-50R to 14-50R. The three wire versions were introduced during WWII to conserve metal by using the three wire cables instead of four, with the understanding they were somewhat less safe but the metal was needed elsewhere. Due to lower installation cost for builders, they managed to keep the code exception around until 1996.

The safety issue in question is that in the 10-30 configuration the ground and neutral share the same wire and the same prong in the cord which means that metal chassis of the appliance is bonded to the neutral conductor, which like the hots, carries current. If/when the neutral wire gets loose, corroded, cut, etc and either of the hot wires remains intact then you will now have a floating potential on the appliance chassis of up to 120V with respect to earth. This means that you can touch the dryer with one hand and the properly grounded washer or plumbing right next to it and get a serious shock. The newer 14-30 circuits have separate ground and neutral conductors and require that the neutral conductor is isolated from the appliance chassis making it much safer in the event the cable or plug becomes partially damaged.

You may think it's rare for only the neutral conductor to burn loose, but I have seen dozens of this exact situation so it really does happen in real life.

But alas, the BORGs don't sell anything longer...'safety' issues once again. Which I understand all of the above to prevent some bozo from wiring a 100ft extension cord, but we really can't go just a few more feet on these cords?

The issue is the 10-30 devices are now listed as "replacement only" so it can only legally be sold as an exact replacement of an existing part. There's a good chance their suppliers don't even produce the 10-30 cord caps anymore. The prefab 10-30 cord sets are used to install new dryers in pre-1996 homes, but other than that there's no legal use for a 10-30.

With all that said, this is not as big an issue for 240V power tools as it is for ranges and dryers because power tools typically only have one 240V motor and no 120V components which would introduce a current on the neutral. The hazard in dryers and ranges exists because those appliances have a mixture of 240V (heating element) and 120V (drum motor) loads powered from the same cord.

  • Author

My friend dropped in and helped wired it up and dealt with the neutral part pretty much as expected, the only oddity was that the motor was running despite the switch being off. When tested again with a meter, current was running through the switch and it was concluded it was bad (who knows how old that was). Swapping it out for a new one resolved it, all connections tested with the meter and the motor runs fine. The jointer, eh...not so much yet thanks to a stripped bolt but that disaster is in another thread.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Who's Online (See full list)

  • There are no registered users currently online

Forum Statistics

  • Total Topics 32.1k
  • Total Posts 437.6k

Member Statistics

  • 26,012 Total Members
  • 3,644 Most Online
  • JAR Newest Member ·

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.