STL Woodguy Posted July 3, 2012 Report Posted July 3, 2012 You might have seen my other topics asking all about my new jointer and this topic is now outside of the subject lines (as I'm now going in the other voltage direction), but if not, I bought a used Powermatic 60 jointer the other day which is wired at 220v, but can be switched to 110v. I considered using my dryer port, but hit a brick wall there involving short dryer cords (more in second half of 220v thread). No matter, I think it's best if I just went 110v with it anyway. Which I had no clue on how to do at first as the manual said nothing, until I found the schematic above the motor's junction box. Once I saw that, the light bulb went off in my head. Now I think everything is making sense, but I want to make absolutely sure I understand the following correctly before I execute everything. (I'm also showing the following to a coworker tomorrow who understands electrical work and is bringing me a free cord to boot.) I drew up the following in Illustrator: this illustration shows how my jointer is currently wired up at 220v. Two things threw me at first, the first being the cords wired up differently...but the diagram says to reverse 5 and 8 for the rotation, and indeed it is cords 5 and 8 backwards to spin the cutterhead the right way on the jointer, I imagine. The other thing was that the large light brown cord going from the switch to the junction, but I assume that's the same thing as the white cord. Anyway, here is what I am thinking for 110v.... So first off, do I understand this correctly? Second, is it necessary to also replace the cord going from the switch to the junction, or it's just switching out the cord with the plug going to the switch? I think someone suggested a 10-2 cord before, is that appropriate to use here? (The motor says it uses 16 amps at 115v.) And can I still use the same switch, or does that need replacing? Quote
PaulMarcel Posted July 3, 2012 Report Posted July 3, 2012 Yes, you have that correct. For your questions: (leftmost question) Which gauge is the cord? It should be at least 12ga. As it was wired for 220V, it could have been 14ga, but that's pretty unlikely. People usually use the tail given with the saw and that would always be the largest gauge it could need. (top question) Line to the NEMA-5-15... if the motor states it uses 16A at 110V, you have to account for a motor surge of 18%. Peak will be 18.8A. You need a 20A circuit for it. Granted, it won't take maximum amperage all the time, but that's its stated requirement. Therefor you should use a NEMA-5-20 (one tab has a T) although I find a lot of things requiring those being sold with 5-15s. (middle question) You can generally use the same switch; look on the back and it should give a voltage range. Usually a switch is just that: something flipped to make a connection. The limits will be embossed on it. Some of those nice magnetic switches you can get aftermarket with a kick paddle are nice because some won't come on until turned off in the case of a power failure. So a quick turn off will leave the tool off and not suddenly start it back up. Nice diagram. EDIT: forgot you are in a basement. If your circuit is a 15A circuit, you don't want to just swap the breaker out at the service panel for a larger breaker without verifying things. If you pull the 110V socket out and look at the lines going to it, if they are 12ga, you likely could upgrade the breaker. Point is that you need to verify things before upgrading a breaker. Usually wall sockets always allow for 15A but might have been cheaply installed with 14ga. Can be the case if a basement was finished after construction. Quote
Mike M Posted July 3, 2012 Report Posted July 3, 2012 Most of the circuits in a house are only 15A. The only exceptions are usually in the kitchen. Unless the house was custom wired, the 15A circuits are wired with 14 gauge which is not suitable for 20A. Also, as mentioned above, your jointer is going to draw close to 20A at startup. If there is anything else on the circuit such as lighting, a 20A circuit will trip when you start the jointer. You would be better off making making a converter for your 220V dryer socket. Purchase an appropriate dryer pigtail, an electrical box and a 220v-20a socket and wire them together. Also add a 220v-20A plug on the end of the jointer cord. If the dryer socket is the older 4-prong type, leave the common (white) wire unconnected in the box. You can even buy a double box and wire in 2 - 20A sockets to accomodate your saw too. Mike Quote
STL Woodguy Posted July 3, 2012 Author Report Posted July 3, 2012 As mentioned in the 220v thread, I can't find a lone plug (to make my own cord) for a three prong 10-30 dryer port, repeatedly told they don't make them for safety reasons, they only make the plug + cord. I also can't locate any cord longer than 6', once again told they don't make them due to safety reasons. I suppose a 10-30 cord of the extra needed length (need 8-10' total) could be soldered / attached to the end of the dryer cord, but that makes me nervous. Also, I am a renter, so there will be no tampering with the electrical box itself. I wonder if the socket in my basement is higher than 15a, as that socket is normally intended for big things like washers, etc. For what it's worth, I've plugged my table saw, band saw, etc into it and never had an issue, no flickering lights, etc. I only ever run one single thing off that particular port at a time and swap cords as I need machines. Quote
STL Woodguy Posted July 3, 2012 Author Report Posted July 3, 2012 (leftmost question) Which gauge is the cord? It should be at least 12ga. As it was wired for 220V, it could have been 14ga, but that's pretty unlikely. People usually use the tail given with the saw and that would always be the largest gauge it could need. (top question) Line to the NEMA-5-15... if the motor states it uses 16A at 110V, you have to account for a motor surge of 18%. Peak will be 18.8A. You need a 20A circuit for it. Granted, it won't take maximum amperage all the time, but that's its stated requirement. Therefor you should use a NEMA-5-20 (one tab has a T) although I find a lot of things requiring those being sold with 5-15s. (middle question) You can generally use the same switch; look on the back and it should give a voltage range. I talked with coworker and showed him the illustration, you are correct: we will go 12 gauge on the wire. He also said if the switch was good enough for 220v, it would work fine for 120v (but not necessarily the other way around). The only thing up in the air is that outlet, whether it's 15a or higher like 20a (I probably should have found that out first), I'll investigate over the holiday. My coworker says it should be fine so long as I'm not trying to run anything else off of it at the same time. I believe my table saw is 15a, since it would surge a bit on startup I assume that would raise the amps, yet the outlet has never popped the breaker during startup or during operation. Quote
Joraft Posted July 3, 2012 Report Posted July 3, 2012 ... He also said if the switch was good enough for 220v, it would work fine for 120v (but not necessarily the other way around). That's not necessarily true, switches are generally rated for amperage as well as voltage, and by converting the motor to 120v you will be doubling the amperage load on the switch. If I were doing this, I would do whatever it takes to adapt the machine cord to the dryer outlet. Running at 220v will draw half the amperage and therefore be twice as efficient, and there will be no worries about breakers or wire size.. Quote
rmac Posted July 3, 2012 Report Posted July 3, 2012 I agree that you should leave it set up for 220. I have a plug like the one you need in my junk drawer. PM me your address and I will mail it to you and you can get on with your life. -- Russ Quote
STL Woodguy Posted July 3, 2012 Author Report Posted July 3, 2012 if you get the nema code from the socket, you can order the plug from mcmaster-carr. HA, had a feeling the BORG employees were full of it (to a degree). I just ordered a 10-30 plug off of there. (No need Russ, but thank you for the offer.) So going back to the 220v diagram, it would just be a matter of just changing the head, correct? EDIT: Will this work though? The NEMA 10-30 plugs - as I understand it - are hot, hot, neutral, while the machine is expecting hot, hot, ground...is using the neutral as the green ground cord safe? Quote
PaulMarcel Posted July 3, 2012 Report Posted July 3, 2012 Most of the circuits in a house are only 15A. The only exceptions are usually in the kitchen. Unless the house was custom wired, the 15A circuits are wired with 14 gauge which is not suitable for 20A. Good point on the 14ga. I've added circuits on bathroom circuits and surprisingly enough they were 12ga on a 20A breaker (so I'm set if I ever get a blowdryer!) But the two closet circuits were 14ga. Rest of the thread is right, though, don't trust basement wiring; verify it cuz you have no idea when it was put in. Quote
STL Woodguy Posted July 4, 2012 Author Report Posted July 4, 2012 I talked to the guy at Woodcraft about it who had a lot to say on the subject. Won't go over it all, but his recommendation was that 110v for the jointer would be perfectly fine even on a 15a port - so long as that was the only thing on the port - as 16a was the maximum the jointer would draw and not likely to be pushed all the way to the max, especially with such light cuts. Despite the spike in power upon startup, that would be extremely brief. To be honest, I have a hard time arguing with that logic: my table saw is 15a and 1 3/4 HP like the jointer, and I never have had issues running it or surging things at all, and that has made far more aggressive cuts than what I expect the jointer would do if set to 1/32 or 1/16. But that doesn't matter either way: it turns out that Lowes DID have the 10-30 plugs I need to go 220v after all. The sneaky thing was that their 10-50 plugs (three straight prongs at angles) includes a 'L' plug that can be swapped out. The bag on the back says it's for both 10-30 and 10-50. Bought a 12-2 cord with the exact length I need, and I have a feeling I'll be in business soon. But my final question stands above, I should be using the 'L' (neutral on a 10-30) simply to ground, right? Thanks for all the advice in the electric threads (especially Paul), it's been very educational and I know more about electric now than I care to know Quote
PaulMarcel Posted July 4, 2012 Report Posted July 4, 2012 I think this group of threads has changed directions in the past 24 hours more times than I have changed underwear. For the sake of clarification, because someone may not collate these threads and read something in isolation, the 'L' is neutral on that plug. The fact that it is going into a dryer receptacle (and assuming everything was done to code) means that neutral line is guaranteed to be connected to ground in the service panel for the purpose of grounding the equipment (so called system ground). As a rule, 'neutral' is never 'ground' for the purposes of wiring. 'Ground' should never have current flowing on it (if so, you have a ground fault that a GFCI catches). 'Neutral' is poorly named; a better name would have been 'return' because that's how current gets back to the service panel. If you don't think neutral has current, stick a flat-blade screwdriver in the wide slot of a plug. You should get some feedback. Other caveat: unplug the dryer and plug in the jointer; don't make a pigtail or something to have them both connected at once as that 'system ground' is intended to tie to a single piece of equipment. When we briefly mentioned installing a surface-mount box, you would have been tying to real ground for the grounding pin. It may have been easier overall to get a Veritas jointer plane. Quote