Hi all!

 

I have an old electric water heater that I think would be just perfect for supplying steam to a box. So you know basically what I am thinking about, I would cut the tank to form a bowl, and direct the steam into the box by some means.

 

It looks like I could connect the element to a switched 220v line, without a thermostat, to enable continuous heating. The diagram shows a ground from the line, but I am not sure how I would ground the tank so I don't get fried.

 

Does anyone have any suggestions?

 

Thanks

The bare ground wire should attach to a lug on the tank itself. I also think you are likely to get better steam action if you leave the tank intact, and just pipe the output line to your bending box. However, under no circumstances should you allow te tank to become completely sealed. Doing so would create a bomb that will surely kill you. Also, I'm pretty certain that steam creation will be a slow process, unles you have a very small tank to heat.

I recommend that you browse discovery.com/mythbusters, and look for clips of the multiple episodes they did, where they validated the explosive power of steam under pressure....

==> connect the element to a switched 220v line, without a thermostat, to enable continuous heating.

 

Not so sure that's a good idea...  You'll need to check the duty rating for water tank elements -- I doubt it's continuous duty...  I believe impulse heaters are duty-rated against some sink...

  • Author

Thanks everyone for responding.

 

The tank is about 20" dia x 5' tall, so I pretty much have to cut it off for the steam to rise into the box. Also, having grown up hearing tales of exploding pressure cookers, I don't want to take a chance on some crazy critter plugging up the pipe. I guess some sort of lid just laid on, with about a 2" pipe flanged to it, would do the trick.

 

It's too bad I didn't take pictures when I stripped the thing. All I wanted was the tank to make a couple braziers. Too often I wind up kicking myself because with digital the only cost is the few seconds it takes to snap a shot.

 

So, you think all I have to do is to connect the ground directly to the tank? It makes sense, but I am having trouble visualizing it. Please have a look at the photo and tell me what you think.  

 

Regarding the element burning out: 1) It would be interesting to see if it would keep going for two hours, and 2) I don't care if it burns out, because it is scrap anyway. All I am really concerned about is not electrocuting myself :-)

 

But what do you think of connecting it to a 110v line? How would I do that? It seems like it might last longer, though it would take longer to boil the water.

post-14419-0-10750600-1377731542_thumb.j

Connecting a heating element designed for 220 volts to a 110 volt circuit will result in only half the power / heat output. Perhaps even less, if the temperature coefficient of the element isn't linear with the applied voltage. You may never get the water to boil.

Regarding the ground / earth wire, look for a lug on the tank to connect it on. The part you can touch, the tank shell, should be well bonded to the earth that you are standing on so that there is no potential difference (voltage) between you and the tank. I also highly recommend using a ground fault circuit interrupter for anything involving electricity and water. If you don't know what that is, find an electrician that does, and ask for his/her help. You are courting death here...

  • Author

Thanks again. I think I am getting the picture. Connect the tank to the ground wire and also directly to the ground. I think I will get really crazy about it, using two 8' rods connected in series and spaced about 10', as with a main electrical panel. And the GFCI is also a great suggestion. In addition to providing protection, it will also be a good way to verify that the circuit is correct. I think I will incorporate additional protections, as well. Like a main disconnect inside the garage, non-conductive shielding around the tank, and a raised wooden walkway... either that or go with gas :-) But thanks for helping me get my head around this problem!

The GFI could cause issues with nuisance tripping.  They are also very expensive for a 220v gfi.  Theyre even more expensive to get the the class b GFI that are rated for these kinds of tasks.  The only reason i know and even bring this up is because early in my career I installed a pre-fabed heating tape on a guys roof and we constantly had problems with the GFI tripping.  After switching to the more expensive class b GFI no issues.  The class a GFI devices  are rated to trip at  if i recall 3 milli amps and the class b devices are rated at 10 milli amps (or close to it)  the problem with the lower mili amps GFI is the resistance in the heating process.  The GFI measures input and output of its current and if it deviates more than the 3 milli amps or so it will nuisance trip.   Not that i dont want you to be safe, I just dont want to see you have a headache either.  I always encourage the use of GFI outlets around water, however I will point out they dont require a GFI circuit for a new home to have an electric water heater and if they thought there was an issue or reason they would.  OF course they also arnt modifying their brand new electric water heater either.  HOPEFULLY you can get by with a class a GFI (class a is your typical GFI rating)  but id be prepared to get a class b if needed if your heart set on the GFI protection.  For grins and giggles price both, and no you wont be able to get a class b GFI at your hardware store more than likely youll have to goto an electrical supply house and they may even have to order it for you.

 

I think youd be best served by making sure the grounding is correct, the wiring is correct, and making sure the shell, frame, and tank are all bonded.  You can check this by doing a simple continuity test between something thats  properly grounded and alternating the testing probe between the shell, frame, and tank as well as anything else you want to check while maintaining the other probe on the ground you are using.

 

I would also suggest running a slightly larger grounding wire #6 copper should suffice.  if you do ground rods make sure they are flush to the earth, 6' or more apart from each other, driven straight into the ground.  One ground rod would honestly more than suffice.  Not that theyre expensive, but they are back breaking to drive into the ground.

 

I think if you hook it upto a 110v outlet it wouldnt work and I agree  If it does work it pry wont work well or for long and certainly not efficiently.

 

 

If you have any other questions shoot me an email or pm.

 

Nyles

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Forum Statistics

  • Total Topics 32.1k
  • Total Posts 437.6k

Member Statistics

  • 26,012 Total Members
  • 3,644 Most Online
  • JAR Newest Member ·

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.