Clearvue CV1800 Wiring

Featured Replies

I am preparing to have a licensed electrician come in to install a dedicated 240V/30A breaker for a Clearvue CV1800. I have searched this forum and others to make sure I know exactly what to spec since there are thousands of different situations. Even though he is the expert I just assume he is not typically installing a 5HP motor...

 

Here is what I understand I need to wire up the CV1800 with the purchased CV electrical box.

 

8/2 awg with a 240V/30A breaker. Do I need to install a GFCI since it is in the garage? Does this mean a 30A GFCI breaker which is extremely expensive? Or is there a different overload protector?

 

Anything else?

 

Also planning to run a 240V/20A and 2 120V/20A circuits. Assuming these all have to be GFCI protected and can all have multiple outlets? Assuming the first one needs to be a GFCI.

 

Any good books to help me out. Planning on roughing in the wiring and letting the professional do the hooks ups and inspection.

 

Thanks!!!

 

 

As far as GFCI and such, a licensed electrician should know the code requirements for your particular structure type, location and electrical requirement.  In order to be compliant (and therefor safe) he just needs the circuit requirements.  Wire gauge and type, dedicated versus multiple outlets per leg will all fall under code for your particular situation.  You're paying a pro, I would trust his decisions.

I had an electrician come in and set mine up Derek.  I gave him my CV manual and an overview of the outlets and uses.  From there, he set everything up from installing a 220 circuit to the CV electrical box to wiring the motor.  He was only there for about an hour.

  • Author

Thanks Gee-Dub and Tiods! I trust the professional, but I live under the trust but verify slogan. It is helpful to hear from others that have had it installed as well.

My only concern is the electrician thinks I only need to run 10/2 for about a 50ft run, however based on reading the most exciting book on the earth. . . NEC handbook, it states 5HP motors require 8/2. Do you know which gauge your cyclones are installed with?

I don't recall but, I do know that the electrician followed CV's recommendations.  Perhaps you could download the manual and have a look.  I believe it's a free download..

  • Author

I have read the "assembly instructions" on CV's website. However there isn't a mention of requirements. I have asked Cathy from CV if there is a more in-depth version. Thanks!

1 minute ago, Derek_PNW said:

I have read the "assembly instructions" on CV's website. However there isn't a mention of requirements. I have asked Cathy from CV if there is a more in-depth version. Thanks!

She's the same one I dealt with, she's usually pretty quick with responses.

  • Author

She has been great and very responsive. Just a few months ago I was talking with her about when the CV06 would be in-stock. . . It still is not in-stock. . . so I guess I am buying the CV1800? What a great up-sell tactic on CV's part! :D

Now all I want to do is read and talk about the install. . . haha

You're welcome to take a drive up to my shop and see it in person if you'd like.

  • Author

Also noticed. . . there was no sales tax on my purchase. I had to double-check my address so I wasn't surprising someone with a free CV1800!

Just now, TIODS said:

You're welcome to take a drive up to my shop and see it in person if you'd like.

I forgot you were in Washington! I might be very temped. Plus I just like to see how other's have set thier shops up!

1 minute ago, Derek_PNW said:

I forgot you were in Washington! I might be very temped. Plus I just like to see how other's have set thier shops up!

Just a couple hours North of you..  Drop me a PM if you want to come up..

  • Author
1 minute ago, TIODS said:

Just a couple hours North of you..  Drop me a PM if you want to come up..

I extend the same invitation to you as well! Business travel this week, but I will send you a PM. 

Off-topic, maybe we should find some time to get the Washington folks together?

2 minutes ago, Derek_PNW said:

I extend the same invitation to you as well! Business travel this week, but I will send you a PM. 

I'm currently gone for work as well but, will have some time at home here very soon.

6 hours ago, TIODS said:

Just a couple hours North of you..  Drop me a PM if you want to come up..

@Derek_PNW It is well worth the trip.  I learn something new everytime.

 

On 4/17/2017 at 9:00 AM, Derek_PNW said:

Thanks Gee-Dub and Tiods! I trust the professional, but I live under the trust but verify slogan. It is helpful to hear from others that have had it installed as well.

My only concern is the electrician thinks I only need to run 10/2 for about a 50ft run, however based on reading the most exciting book on the earth. . . NEC handbook, it states 5HP motors require 8/2. Do you know which gauge your cyclones are installed with?

Derek, what electrician are you using? I still need to get someone over to my house to give me an estimate on a sub-panel. I have been putting it off because I am scared of the price they are going to spit out.

 

On 4/17/2017 at 9:22 AM, Derek_PNW said:

I extend the same invitation to you as well! Business travel this week, but I will send you a PM. 

Off-topic, maybe we should find some time to get the Washington folks together?

I think this is a great idea!

 

On 4/17/2017 at 9:25 AM, TIODS said:

I'm currently gone for work as well but, will have some time at home here very soon.

Mind if I tag along. Love learning from more experienced woodworkers. I grew learning from my dad and he is 3000 miles away.

 

Matt

5 minutes ago, MattF said:

Mind if I tag along. Love learning from more experienced woodworkers. I grew learning from my dad and he is 3000 miles away.

 

Matt

 

 

C'mon up Matt..

  • Author

@MattF I am using Mountlake Electric. He is asking about $100/hr and was happy to inspect my work and do the final connections so I don't kill myself.

 

@MattF we will have to plan a trip to visit@TIODS.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Forum Statistics

  • Total Topics 32.1k
  • Total Posts 437.6k

Member Statistics

  • 26,009 Total Members
  • 3,644 Most Online
  • Joseph b Newest Member ·

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.