anyone know if it affects tools differently if you use a heavier gauge extension cord than what is recomended?

i.e. ridgid 2412 table saw 15 amp on a 14 gauge cord vs. the same saw on a 12 gauge cord?

Posted

resistance is related to cross section & length. So a longer cord should be heaver gauge to reduce resistance (voltage drop) between panel and motor. Rule of thumb, you want to keep voltage drop below 5%. Many folks use 1 gauge heaver than specified to reduce potential for drop. Also, use as short a cord as safe, extra length give more resistance.

Posted

It probably won't make a difference to the saw in general. It is what is recommended by the manufacturer. I always think of worst case scenarios where the tool is really working though. Manufacturers subscribe to the least possible specification. Bottom line is, get the heaviest guage extensions you can afford and just enough length that you realistically need. There are some really nice heavy duty ones out now with a silicone jacket on them. I think they call them contractor cords around here. You can tell by the more vivid colours of the cord itself ( watch for knock offs). Also, take care of them, learn how to coil the cord without putting twist in it. 12 ga is no good to you if a bunch of strands are broken.

http://www.blinkx.com/watch-video/how-to-wrap-microphone-cables/hvjN1SueH-4Xi3DsQUmS7w

Posted

DISCLAIMER...YOU'VE HEARD OF SHADE TREE MECHANICS??? I AM A SHADE TREE ELECTRICIAN. I can do the basics. Solid wire vs stranded. The stranded can transmit almost as much juice as the solid but not quite and like has been said, you could have broken strands. Having burned up a few tools in my time with extension cords, I wire everything in the shop with solid wire with 12 gauge. If it is a motor pulling some amps, and if it's even a question in my mind, go with a heavier gauge wire (i.e.10 gauge wire). So it cost me $5 more dollars; it saved a $400 motor. I am feverishly working to eliminate E cords in the shop....and wood giblets, and the bolt that was dropped, and CRAP!!! :o ....I want the wheels to roll freely and the feet to land on good smooth concrete.

Posted

I've been on tons of jobsites with extension cords running everywhere. As long as the gauge is big enough for the run and needed amperage, you're set. Just remember, it DOES need to be plugged into a proper outlet and some house typical outlets are only 14 gauge wire.

Posted

==> some house typical outlets are only 14 gauge wire

probably up to 50% in most households.

This is why my electrician says space heaters are so dangerous today. They need a 20 amp service, which requires 12 gauge wire and a 20amp outlet. Rare in today's residential structures.

Posted

most of my 20a devices have the 20a horizontal lug (nema 5-20), but not all. that is probably part of the problem. if you enforced the nema plugging conventions, there would probably be fewer fires -- but fewer sales (you cant plug a nema 5-20 device in a 5-15 outlet).

about 9/10 of my outlets are 12g nema 5-20, but then again, i specified the wiring for the house :)

my shop wiring is all 10g 120/240 (most tools 5hp) with 8g for 3 phase (7.5hp).

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Who's Online   2 Members, 0 Anonymous, 50 Guests (See full list)

  • Forum Statistics

    32.1k
    Total Topics
    437.6k
    Total Posts
  • Member Statistics

    26,009
    Total Members
    3,644
    Most Online
    Joseph b
    Newest Member
    Joseph b
    Joined