The 220 in my shop is on a 50 Amp Fuse...

Featured Replies

The title says it most. but to review:  

 

I had new service pulled to my house, and a new box installed.  I said to the electrician I wanted 220 pulled to my shop as well as a separate 110 circuit for the other power tools.  I guess out of habit (and because I didn't know any better) he set up the 220 in the shop on a 50 Amp fuse in the service box.

 

I have since read that it's a bad idea to put my 220v table saw on a 50A fuse because if there's a problem the motor will burn before the fuse blows.  Also, the plugin he installed is for a 220 50A.  One of those big round twistlock plugs.  Obviously I can change the socket out, but again, I've read that you really shouldn't' put a 30A socket on a 50A fuse.

 

What can I do short of hiring another electrician to come in and install a sub panel, or re-wire the service box so that it's no longer on a 50A fuse?

 

Thanks in advance.

 

Morgan

 

 

 

Breakers are for protecting wiring in the house period. Motor protection is or should be built into the machine or on cheaper motors built into the motor. It is fine to plug into a higher rated plug. As a matter of fact you need more amperage available than the tools name plate otherwise you will trip out the breaker all the time.

Steve

Depends on the saw you're using.  My 5HP Powermatic calls for a 50A  breaker..  A 3 HP would not; it all depends.  Worst case, you'll need to swap out breakers and plugs.  The wiring is rated for 50A so no concern of overloading the wiring.

If you only need the one tool on a 220 volt circuit, you are good to go. However, having a 50 amp supply means that you could install a small sub-panel and connect more than one 220 volt machine. Need to be certain the wiring between your main panel and the sub-panel is rated for the current you machines will need, but if you electrician followed the NEC and local building codes, that should be fine as well. Did you have your local building inspector take a look?

5hp should be fine on 30-40amp circuit. The name plate should show the full load amps. It should be about 22-25. The overload protection on the machine should be pre-set so don't mess with it.

Steve

  • Author

A couple of follow-ups:

 

1.  The wiring was done to code and was inspected.

2.  Saw I'm using is currently 1.5 buying a 3HP soon.

 

wtnhighlander, am I reading you correctly that if I wanted to plug in more than one 220v machine I need a sub panel?  I thought I could just put in a two-socket plug receptacle.

A couple of follow-ups:

 

1.  The wiring was done to code and was inspected.

2.  Saw I'm using is currently 1.5 buying a 3HP soon.

 

wtnhighlander, am I reading you correctly that if I wanted to plug in more than one 220v machine I need a sub panel?  I thought I could just put in a two-socket plug receptacle.

 

Sort of but not really. Sounds to my like you had an electrical  run wire and install just a 50a outlet in your shop. This is sort of a waste for a hobby shop. Your 3hp tablesaw will run fine with a 20a breaker. Your going to be better off adding a sub panel and making use of the 50amps with different circuits. You could install two smaller ones, one for the table saw and the other for maybe a dust collector or something along those lines. Small sub panels are cheap and it would not cost much to have it installed.

==> Small sub panels are cheap and it would not cost much to have it installed.

 

+1 -- except that he would have to pull a new 4-wire.... But still not much $$ in the grand scheme of things considering what you gain with a sub-panel...

==> Small sub panels are cheap and it would not cost much to have it installed.

 

+1 -- except that he would have to pull a new 4-wire.... But still not much $$ in the grand scheme of things considering what you gain with a sub-panel...

 

Ya he doesnt say wether its detached or not. If detached he should have a 4 wire pull already but I'd check anyways at the outlet. Most decent electricians will pull the extra ground just because some mechanicals like hot tubs require them.

==> Most decent electricians will pull the extra ground just because some mechanicals like hot tubs require them.

 

that's a good point....  I forgot that sometimes they do that...  I should have known, about 5 years ago, I needed to replace one of my AC compressors -- he pulled 4g/4-wire -- because it was cheaper to get 4g/4-wire copper than 4g/3-wire copper  ...go figure...

Think of it this way.  Every time you plug a 12 amp vacuum cleaner into an outlet in the house, which is either a 15 or 20 amp circuit, you don't have to change the breaker, wire, and receptacle to 12 amps.

Couple of questions.  You say he put the circuit on a 50amp fuse? Does your house main panel use fuses? Or did he put it on a 50amp breaker?   Is the location of the 50amp outlet in a detached building or garage? Or is the building or area attached or part of the main home?

 

Ultimately it sounds like you just need to remove the 50amp outlet he installed and replace that with a small sub panel.  Then off that sub panel install an appropriate 30 or 50 amp plug on an appropriate sized breaker in the sub panel.  You can then add a 110v general purpose outlet circuit (lighting, 110v outlets etc) off that sub panel on its own breaker as well.  So your 50amp 'fuse' will protect the wiring from the homes main panel to the sub panel.  The sub panel breakers will protect the wiring to each individual equipment or device.  

 

To my knowledge they do not make a duplex 50amp recepticle or even a duplex recepticle rated for more than 20amps.  So as far as I know, no you will not be able to swap it out to have 2 220v outlets.  

 

Couple of things to keep in mind:  Due to the size of the circuit that was already ran out there I wouldnt get that big of a sub panel, If you stay with a sub panel that has fewer than 6 breakers I believe you can forgo having to have a main disconnect at the sub panel and that will save you some cash on the sub panel purchase.  If you want a main breaker you can go ahead and get a sub panel with one it wont hurt.  If you plan to have more than 6 breakers in the enclosure then make sure you get a sub panel with main breaker.  When pricing your sub panels keep in mind if it comes with a main breaker or weather you will have to purchase one in addition too.  That really cheap deal you see might not be that cheap if you have to buy a main breaker for the sub panel.  There are other work arounds for this part of things but I dont want to confuse you.  in addition to the main breaker youll pry want to get an extra grounding bar kit for the sub panel as well.

 

For any new wiring circuitry you are doing you can use 3 or 4 wire for the wiring to the equipment.  It really comes down to the grounding and the receptacle and the plug.  Both wires will work, most people and companies these days use a 4 wire but theres plenty of 3 wire stuff installed daily on existing stuff.  I would personally just match the receptacle to the equipment plug and then get the appropriate sized wire with the appropriate number of conductors. .  Running a 4 wire and using  3 of the conductors is fine too, Just tuck the extra neutral (white wire) away in the back with a wire nut on it.  If you match your new receptacles to your existing plug setup youll save a few bucks having to replace any plugs on your equipment.  Just make sure if your equipment requires a 4 wire (which I doubt) that you run the 4 wire otherwise you gotta cheat and you dont want to have to do that.

 

The wiring to the sub panel depending on a few factors should be 4 wire (used to be able to use 3 wire now you have to separate the neutrals and grounds thus requiring a 4 wire instead of a 3 wire).  I am hoping and assuming that the electrician ran a 4 wire to the 50amp outlet he installed and that you can swap a sub panel right to the existing wiring.  Otherwise you have to get creative or you need to add a wire or re-do the wiring all together.  Few points regarding this:  If you want a bigger (more juice) sub panel go ahead and replace the wiring with the appropriate size conductors and 4 wires. I would suggest not getting 'creative' while we can make it work and its the way it was done for a long time, it technically wouldnt be upto code so I dont suggest it.    Although you could I suppose install the sub panel make it work, then if it was ever an issue just remove it and replace it with the 50amp outlet that was originally there.  Pretty feasible if its an unfinished area and say you wanted to sell the place in a few years and didnt want the buyers home inspector to raise any issues.....Ultimately I suggest just doing it right the first time.

 

For your new circuits that you may run I'd suggest 20amp for the general purpose lighting and for the bigger amperage outlet I'd possibly look into the cost of aluminum wire,  especially if you have any significant distance to run.  You will need to get a different sized aluminum conductor than a copper one so either ask your hardware store helper or shoot me an email and I can help you size the wire.  If its a short distance and moneys not a big object just use copper 4 wire and then your covered for the future if you get a different piece of equipment or ever re-arrange your shop and plug something else into it.  For the 20amp general circuits youll want to use #12 copper. If you end up needing to replace or add wiring for a sub panel and again if its any length of distance ask or look into aluminum wiring, it works just as well if sized correctly and its significantly cheaper usually.

 

Installing the sub panel has a few do's and dont's but before i break off into that tangent let me know where you are at with things and what your thinking.  If you want to install the sub panel I can help walk you through it if your comfortable or can help inform you so when you talk to the electrical contractor/electrician you get exactly what you want and need.  

 

 

Couple of points on basic electrical theory and equipment: The analogy with the vacuum cleaner is a very good one.  You draw what you draw and thats it.  That means if you plug your 15amp saw into a 20amp outlet your gunna just draw 15 of the 20 amps.  However you can run into problems if you plug something into to big of a circuit (this is the reason they dont just put all your outlets on 1 50 amp circuit all tied together) while your draw might be 'not an issue' if you had any sort of electrical issues with the device or piece of equipment (short circuit etc) you could in theory not create a large enough arc to trip the over sized breaker feeding the circuit.  So if you plug a 15 amp drill into a 50amp outlet and it shorts out the short may not be enough to effectively trip the breaker.  This is because breakers are inversely proportional and require (depending on the ampacity of the breaker) a certain size of arc to trip.  To keep nuisance tripping to a minimum usually they (the breakers) require a certain size to the arc to trip the breaker.  This is the reason why they use different sized plugs and receptacles, to keep that 15 amp saw off a 50amp circuit with out the appropriate over current protection.  In general unless you know what your doing its a good idea to stick with the general rules for conductor sizing and over current protection.  You can have a similar issue with putting to small of a breaker on to big of a wire as the larger wire actually absorbs some of the arc and in turn the arc may not be large enough to trip the breaker.  This could result in say a wire that was arcing and continued to arc possibly causing a fire,damage to the conductors or even worse.  Theres a reason there are rules (and no its not so they can be broken)  and while I dont claim to agree with every one of them most of them were put in place for a reason  to avoid a problem or possible danger.  So yes its fine with in reason to plug in to a larger sized circuit but it has its limitations if your staying within the realm of safety. 

 

Sorry for the rambling.  Im beat down tired and just got off work.  Heading to bed now, will check back in a day or so.  Hopefully I wasnt so tired I misspoke some where.  Will re-read and edit tommorow if i did. ;-)

 

Nyles

 

 

PS -  the reason 3 wires is more expensive than 4 wire is usually a supply and demand.  There seems to be more of a demand for 4 wire so they make alot more of it.  

 

 

 

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Forum Statistics

  • Total Topics 32.1k
  • Total Posts 437.6k

Member Statistics

  • 26,012 Total Members
  • 3,644 Most Online
  • JAR Newest Member ·

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.