Niku Posted May 15, 2014 Report Posted May 15, 2014 My circuit breakers were recently triggered twice by, I think, my table saw. There was no flash, but I was using the saw at the time, and I believe there must have been a short-circuit or other electrical disturbance. I have reset the circuit breakers, but I don't want to press my luck, so I'd like to learn more about the subject before I use the saw again. Can circuit breakers be set off by things like using the saw continuously for too long a period, or having the blade get stuck in a rough patch of wood, or moving the blade too rapidly through the work? This happened while I was ripping a bevel into thirteen 8x2x3 boards, and the last time it happened I was only one foot from completion of the project. I don't know much about this subject, but my thinking is that I may have been pushing the blade too quickly through the wood and causing it to jam. Could this cause a electrical disturbance in my electric panel board? In other words, could this trip a circuit breaker? Quote
Tpt life Posted May 15, 2014 Report Posted May 15, 2014 The hotter conductors get, the more inefficient they become. If you are getting your motor hot and it does not have an over temp breaker on the saw, it is conceivable that you could fault your house breaker. It is also possible that heat expansion in motor components is causing a fault. This is not necessarily what is happening or you would need to wait for the motor to cool before restarting the saw. If you did feed too fast so that the saw stalled, this can easily draw too much current for your breaker if your breaker is rated close to the amperage of the saw. Quote
wdwerker Posted May 15, 2014 Report Posted May 15, 2014 Yes, to big of a load on the motor can cause a breaker to trip. A dull blade or a pinched blade when the wood warps in can overload the motor. Quote
Trip Posted May 15, 2014 Report Posted May 15, 2014 ==>blade get stuck in a rough patch of wood, or moving the blade too rapidly through the work? Yes. Power draw varies with load. The harder the motor is asked to work, the more power it wants to have. At some point, power draw could exceed the branch circuit's protection (breaker). The breaker is there to prevent the load from requesting too much power from moving along the wires (generating heat). To be able to help, we would need some data: make/model of TS, size of breaker, size of wiring (if known), list of any other load on same branch. Quote
wtnhighlander Posted May 15, 2014 Report Posted May 15, 2014 Thermal type circuit breakers can also trip if the circuit is drawing close to the breaker's rated current for an extended period of time. Heat build up causes the breaker to trip at a lower than normal current. Quote
Trip Posted May 15, 2014 Report Posted May 15, 2014 ==>Thermal type circuit breakers can also trip if the circuit is drawing close to the breaker's rated current for an extended period of time. Heat build up causes the breaker to trip at a lower than normal current. Good point. Another point -- breakers can 'go bad' and trip below their rating. However, based on your description, I would suspect that this is not the case. Quote
EdgewaterWW Posted May 15, 2014 Report Posted May 15, 2014 But remember it's not just the table saw (TS) using/pulling power (amps). Say your TS is plug into a outlet and that runs to a 20 amp breaker BUT that breaker also is servicing 1,2,3 other outlets in the shop, you have to add up the amps from anything that is plugged in to all the outlets on that breaker and that is running, lights, radio, shop vac, DC, etc and the saw. And say all that is plugged in adds up to 8 amps and the power tool the TS has a running amp pull of 10 amp and a peak amps of 13 amps, so with the saw running your at about 18 amps on a 20 amp breaker, but when the TS hits a load and it's motor pulls it's max amps of 13, now your at 21 amp and your breaker POPS. I had this problem because I didn't know that the outlets on 3 out of 4 walls was on 1 breaker. Now I have 4 walls and 4 breakers for outlets. Sorry for my lack of proper terms. Quote
Niku Posted May 16, 2014 Author Report Posted May 16, 2014 You people are fantastic. This is much more than I had hoped for, and I no longer think it necessary to call an electrician. I now think that this problem is within my control. All I have to do is to take it easy. I'm in no contest, and it won't hurt a bit to take just a little longer to do the job. No more force feeding for me. I might add that I didn't think I was experiencing short-circuiting, but I didn't know enough about electricity to think of what else could be causing the problem. I hope I never have another problem like this, but if I do, I'll know where to go to get the answers. Thanks again, everyone. Quote