I recently purchased a new table saw and was curious if it's recommended to install a longer cord or just use an extension cord.   I'd prefer to just use an extension cord. The table saw is a 230 volt SawStop PCS.  I have a 12 guage extension cord I was thinking of just converting to work with the stock plug but wanted to see what everyone recommended first.

Posted

I made an extension cord for mine. One look at the inside of the control box made me decide not to replace the cord. And I'm an electrician. I cut the factory cord to about 3' & put a twist lock end on it, then used 12/3 SOOW for the extension cord.

Posted
31 minutes ago, drzaius said:

I made an extension cord for mine. One look at the inside of the control box made me decide not to replace the cord. And I'm an electrician. I cut the factory cord to about 3' & put a twist lock end on it, then used 12/3 SOOW for the extension cord.

Thanks for the response. I hadn't opened the switch, but just looking at the wiring diagram and really didn't want to touch it.

Posted

I did almost exactly the same as drzarius on all my big tools, except they all only have a tail of about 6 inches at the machine.  We move them fairly often, and any longer tails just are more trouble.  Any type of 12/3 cord with the letters SO to start with is okay, and Hubbell twist lock plugs.

There is nothing hard about making up those extension cords, or changing the plug on the machine.  You just have to take your time, and cut very carefully into the cover of the SO cord.  The boxes that the plugs come in have a full sized template, on the back, that show you exactly how much of the insulation to strip off the individual wires.  Use a screwdriver that fits the screws fully engaged in the plugs, and tighten them about as tight as the good screwdriver will allow you to.

Put the black wire on the brass lug, the white wire on the silver lug, and the green wire on the green lug for 120v.   For 240v, it really doesn't matter which place the black, and white wires go.  For 120v, on one end of the cord,  you will have to twist the black and white wires out of the position that they come out of the outer cord cover.  If you don't do that, and put them on the opposite lugs from the other end of the cord, you won't get current flow from a GFCI circuit.

Posted

No worries about the voltage.   I just like the type SO because it's so tough.   I have some that are 35 years old, and still  being drug around jobsites.  I don't really care about the oil resistance of the O either, but all the tough ones like I like start with the letters SO.   For a garage shop I guess it really doesn't make that much difference, but I don't remember ever tripping over an SO cord.  They do drape nicely.   An Inspector came by one of my jobsites once and said," It looks like a county fair with all the SO wire on the ground".

Here's a chart with all the different letters, and what they stand for:

http://www.chem.cmu.edu/groups/bier/procedure_files/general/powercords.pdf

  • Thanks 1
Posted
1 hour ago, Tom King said:

I did almost exactly the same as drzarius on all my big tools, except they all only have a tail of about 6 inches at the machine.  We move them fairly often, and any longer tails just are more trouble.  Any type of 12/3 cord with the letters SO to start with is okay, and Hubbell twist lock plugs.

There is nothing hard about making up those extension cords, or changing the plug on the machine.  You just have to take your time, and cut very carefully into the cover of the SO cord.  The boxes that the plugs come in have a full sized template, on the back, that show you exactly how much of the insulation to strip off the individual wires.  Use a screwdriver that fits the screws fully engaged in the plugs, and tighten them about as tight as the good screwdriver will allow you to.

Put the black wire on the brass lug, the white wire on the silver lug, and the green wire on the green lug for 120v.   For 240v, it really doesn't matter which place the black, and white wires go.  For 120v, on one end of the cord,  you will have to twist the black and white wires out of the position that they come out of the outer cord cover.  If you don't do that, and put them on the opposite lugs from the other end of the cord, you won't get current flow from a GFCI circuit.

And that is an electrician approved tutorial. Very well explained.

Posted
1 hour ago, Chestnut said:

Is SJO cord cutting it too close on voltage limits?

No worries on the voltage, but SJ isn't near as tough as S, but SJ is smaller so will coil up tighter. Whatever you do, don't get SJTW, cause it has plastic insulation & outer sheath that will not stand up to even moderate foot traffic for long.

  • Thanks 1
Posted
5 minutes ago, drzaius said:

No worries on the voltage, but SJ isn't near as tough as S, but SJ is smaller so will coil up tighter. Whatever you do, don't get SJTW, cause it has plastic insulation & outer sheath that will not stand up to even moderate foot traffic for long.

I have a lot of SOOW and some SJOOW and i guess 1 SJTOOW not sure where that one came from. Side effect of every extension cord my dad ever owned being black with yellow plugs. I asked him why when i went to buy my first extension cord and his response was "they are 20 years old and coil perfectly when it's -10F." So now all my cords are black with yellow plugs. The coils perfectly when it's -10 is somewhat important around here.

Posted

Ya, the rubber coils much better at cold temps & lays flat better as well. The cost difference between S & SJ is just not that great. SJ cracks easily when it's cold too.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Who's Online   3 Members, 0 Anonymous, 29 Guests (See full list)

  • Forum Statistics

    32.1k
    Total Topics
    437.6k
    Total Posts
  • Member Statistics

    26,008
    Total Members
    3,644
    Most Online
    Bob44
    Newest Member
    Bob44
    Joined