Hi all,

After multiple forum posts on the issue, then settling, then getting new information on it, I'm once again dumbfounded on how to run power to my shop.

Quickfire stats: Running ~70ft cable direct buried from 200A panel to 100A subpanel in a detached shop (300sqft). No pipes/wires in between the two structures. Using #2 Aluminum, so putting in a 90A (or 100A?) breaker in the panel back up at the house. Interior shop wiring features multiple 120V and 240V circuits. I'm quite future proofed and have wired for the following: dedicated circuit for dust collection, dedicated circuit for air compressor, multiple outlets pigtailed and dotted around just in case - tools hooked up to these would never be used at the same time.

So the question: 2-2-4 aluminum, or 2-2-2-4?

I believe I understand that quadplex is the 'correct' way, but this work is not being inspected. I want it to work, and don't want to kill myself and/or others, but I really need some pragmatic advice here - not just "do it by the code" - because my electrician says 2-2-4 will suffice. I need to know if he's saying that because he's been there done that and it's good enough, or because he's a cowboy who wants to use what Home Depot sell 20 minutes away.

Thanks all

Link to comment
Share on other sites

Mark get a second opinion from another electrician. You don't want to get electricity wrong. You can't see it, smell it or feel it until it gives you a belt. It's not worth risking it.

That way you'll know whether the first electrician is firing from the hip or not.

  • Like 1
Link to comment
Share on other sites

The NEC is there to keep you safe... Stating up-front that you don't want an inspection is a real red flag... If there's a fire or you go to sell the house there's going to be a problem...

 

The second red flag is asking about 3 or 4 wire pulls... It's unlikely you'll earth/bond the outbuilding correctly by surfing the net... Wonky grounds will shorten the life of your tools...

 

Electrics are the wrong area to save money on a shop build...

 

Yes, it'll cost some $$ to hire a pro... But it can save $$ in the long run... I'd hire the pro to pull the permit, run the feeder, set the panel, bond everything and get the inspections... From there, you can do the branches. A pro can work with you to manage costs and they can get kit much cheaper than you can... Remember, not all electricians are evil bastards... The jury is still out on plumbers :)

 

I'll give some input, but I'm going from memory and my last interaction with the NEC was quite some time ago..... YMMV

 

You need ground rods in the outbuilding -- I believe two are now required...

The NEC addresses both three and four wire installs... Most municipalities require 4-wire pulls...

NEC doesn't require GCFI, but many municipalities require it...

The sub's earthing and neutral busses are isolated...

 

My first piece of advice is to get a pro...

My second piece of advice is to get a pro..

 

Good luck.

Link to comment
Share on other sites

I know it can be a PITA, but get a permit and get it inspected. Like others have said, it could save your butt on an insurance claim, or even save your life. I got building, electrical, and HVAC permits for my building, and have inspection passed stickers on my panel door and records with the county. 

Link to comment
Share on other sites

So I guess my house is old and grandfathered . My shop is in a commercial building and there is 3 phase available so can't use it as an example. As slippery as insurance companies are these days you know they are going to blame anything done off permit or not up to code and refuse to pay. So I throw my vote with the rest, get a licencend pro and do it up to code.

Link to comment
Share on other sites

OK, so if I go with 4 wire, does it change what outlets I use inside the shop? I'm not familiar with GFCI outlets.. are they a must or an option? They're pretty expensive!

 

No, it doesn't change your outlets in the shop.

 

Yes, GFCIs are expensive but, you don't need them at every outlet.  Suggest dropping one on each circuit except maybe the lighting which should be on its own circuit.  It should be the first one off the box on each circuit.

 

And, to echo those above, get the permit and inspection.  You can do the work yourself but, it could save your bacon in the long run.  The electrical permit and inspection for my 30 x 50 building was only about 80 bucks.

 

Also, Trip is spot on with the grounding.  Where I'm at, 2 rods are required.

Link to comment
Share on other sites

==>Yes, GFCIs are expensive but, you don't need them at every outlet

It's in areas like this is where my NEC knowledge gets thin and rather dated...

 

Last go-around, used GCFI breakers on utility branches... not sure that's still code...

Also installed panel-based overload and spike protection... Not sure if that's still code either...

 

==>Where I'm at, 2 rods are required.

Someone will have to chime in, but at some point you could use facility water as one of the ground bars... I think that may have changed... My last service work was around '09? and we could use city water plus one bar. Local rqmts: 4-wire pull, 36" trench+conduit, electric and teleco in seperate conduit, no AL, up-gauge every 130'. I forget the rest... BTW, sometimes 4-wire is a lot cheaper than 3-wire because, depending on gauge, they make a lot more of it...

 

==>So I guess my house is old and grandfathered

Grandfathering only carries you so far... I forget the formula, but there's a threshold of change (and it's pretty low) where electrics need to be brought-up to code... Same goes for structure, insulation, etc -- but the thresholds are higher... This is one area where an electrician can pay for himself...

Link to comment
Share on other sites

You can get 3 packs of 20 amp GFCI's for about $30 so not bad. Like TIODS said, put a GFCI as the first outlet on the circuit using the line terminal. You can then use standard outlets downstream using the load terminal. Buy an outlet tester that can also pop GFCI circuits so you can test your downstream connections. Check your local code, but in my area 220 circuits don't need to be GFCI protected. 

Link to comment
Share on other sites

The difference between the two is the neutral.  You have triplex going to a house as a first point.  The neutral is bonded to the ground making it a grounded current carrying conductor.  One you leave the main point you must "float" the neutral.  The ground and neutral will be separate in your sub panel.  You do not bond your ground bar to the cabinet and you do not bond your neutral to the ground. So, secondary distribution panels will have 2 hots, a neutral and a ground.

Link to comment
Share on other sites

==>One you leave the main point you must "float" the neutral

A bit off-topic.. what happens if your service disconnect and main panel are separate? As was the case with my last service upgrade... I know what my installer did, but have aways wondered...

Link to comment
Share on other sites

Code calls for four conductors to a sub-panel.  Neutral and ground are not connected in the sub-panel, as Beerboss said-no bonding strap to box.  Ground rod/rods at the outbuilding, may or may not be required by the local inspector, but usually are.  I'd put them in anyway.

 

A separate main disconnect from the main panel is required when the main panel is not right on the inside of the wall behind the meter.  It's mostly a safety thing for the local fire department, so they can turn the power going into the building off quickly.  If there is a disconnect beside the meter, they know not to go looking for it inside the building.

 

Even if you are doing all the work yourself, I'd still permit it, and have it inspected.  It will be a good thing if you, or yours, ever decide to sell the place.

  • Like 1
Link to comment
Share on other sites

Tom's right, get a permit.  Most...not all...inspectors will work with you if you show you are trying to do the right thing.  I would approach it as asking for an education.  These folks, like most people like to show you what they know if you ask them right.

Most people don't understand the amount of damage a neutral can do.  Many assume it is another ground.  Trust me, it IS a current carrying conductor!  You do not want to get between it and ground if it is under load.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

  • Who's Online   0 Members, 0 Anonymous, 39 Guests (See full list)

    • There are no registered users currently online
  • Forum Statistics

    31.2k
    Total Topics
    422.2k
    Total Posts
  • Member Statistics

    23,784
    Total Members
    3,644
    Most Online
    walo47
    Newest Member
    walo47
    Joined