Fricasseekid Posted September 24, 2014 Report Posted September 24, 2014 I have an older Delta 8" long bed Jointer and a Ridgid 10" contractor table saw. Both of these are set up for 110 volts, but I have a single 220v socket in my shop. Which Of these tools do you think would benefit most from the higher voltage? Quote
knotscott Posted September 24, 2014 Report Posted September 24, 2014 Whichever one has the highest amp draw should benefit the most. If the amp draw is equal, whichever gets the heavier load will benefit most....usually a TS, but IIRC the Ridgid is a 13 amp motor that doesn't pose an overly heavy load to a typical 120v circuit. Quote
Fricasseekid Posted September 24, 2014 Author Report Posted September 24, 2014 Well I trip breakers with my TS from time to time while milling reclaimed oak timbers. Quote
Dave H Posted September 24, 2014 Report Posted September 24, 2014 Is this circuit a 15 amp or, 20 amp? A 15 amp is to small a circuit for that heavy of load and, is probably taxing your saw( not good) so yes it would be better to go to 220v also are you running the saw off an extension cord if you have a 20amp circuit but are using a 14 ga. cord that could be the problem I don't use any extension cord thats not at least a 12 ga. also use the shortest extension cord that can reach the machine. 1 Quote
CessnaPilotBarry Posted September 24, 2014 Report Posted September 24, 2014 I prefer to run 220v to any tool that is capable of using it. Like Scott said, 220v greatly reduces the current draw. A lower current draw means your tool gets everything it needs, without as much suffering from cable losses. If you need one, there are 220v extension cords. Think "generator", while walking your home center... Since 220v tools draw less current, approximately half, they can be less affected by an extra 10-20 feet of wire. If necessary, you can choose a common connector for your shop, so multiple tools can plug into the same plug, just pick one that is rated suitably for the tool with the heaviest current draw. In my basement shop, I use my dryer plug for a heater, as I don't really need both at the same time. People frequently share a 220v outlet between things like compressors and welders, because they don't use both at the same time. Quote
Boatworks Today Posted September 24, 2014 Report Posted September 24, 2014 IMO if you're looking for something to fill that 220v hole, I'd look at planers if you don't already have one . Quote
Fricasseekid Posted September 24, 2014 Author Report Posted September 24, 2014 I do have a lunchbox planer. I can't afford anything big enough to run 220. Quote
Mzdadoc Posted September 25, 2014 Report Posted September 25, 2014 Like mentioned above one outlet multiple tools. My table saw and air compressor share one since I'll never be using more then one tool at a time. Something to keep in my if you're popping breakers is unplug tools not being used. They draw even if they're just plugged in. Something I was told. Quote
wtnhighlander Posted September 25, 2014 Report Posted September 25, 2014 Pretty unlikely you will be using jointer and saw at the same time. I vote for running both on 220! 2 Quote
knotscott Posted September 25, 2014 Report Posted September 25, 2014 Pretty unlikely you will be using jointer and saw at the same time. I vote for running both on 220! That's true, which makes it a great idea IMO. Quote
tim0625 Posted September 25, 2014 Report Posted September 25, 2014 I'm a one man shop so I'll only have one tool running at the time. I don't hesitate to put two tools on the same 220V line or even the same 110V line IF the breakers for each one are the same size. Quote
4-Square Posted September 25, 2014 Report Posted September 25, 2014 <Well I trip breakers with my TS from time to time while milling reclaimed oak timbers.> It’s great that the breaker is doing its thing, but there’s another issue in here: breakers wear-out and can fail… Residential breakers are typically rated for a mix of full-load/no-load activations tallying roughly 10K cycles (if I remember my NEC)... However (if memory also serves), the rated number of fault cycles (trips) is somewhere around 50 -- that's five zero, not 50K. Like activations, this number is comprised of a mix of fault-types (overload, neutral, short, etc) so can be a bit misleading. Various types of trips place varying stress on a breaker, so you may get a hundred overload-trips and the breaker can still be AOK, but maybe not… The good news is that breakers are designed to fail-open… But where there is good news, there is bad: a breaker's trip-point tends to drift lower with subsequent trips and breakers don’t always fail-open... So a word to the wise, if you’ve get breakers that trip frequently, fix the load problem asap... and don’t just live with tripping breakers – it’s not safe… Also, if a breaker has been frequently tripped, spend the $15 for a new one… One other point: if this is happing in a small comercial shop it falls into a completely diferent category... In the comercial world, there is specific legal liability attached to tripping breakers. I really don't remember my NEC on this area, but I think the number of allowable trips is in the single digits -- I seem to want to say six, but I also want to say two (I suspect it's six up to a certain amperage and two beyond, but I never remember) -- point is -- it's a low number and you are legally required to replace the breaker (CFR10) ---- and you can get in deep do-do if there is a fire -- meaning it won't be covered by insurance, you could be subject to a hefty fine and you can end-up in the pokey if someone gets hurt... Quote
Fricasseekid Posted September 25, 2014 Author Report Posted September 25, 2014 In my experience breakers start to trip more easily as try wear out and eventually they just won't reset. Not saying to always goes that way. That's just what has happened to me in the past. Quote
Mad Hungarian Posted October 2, 2014 Report Posted October 2, 2014 ...If you need one, there are 220v extension cords. Think "generator", while walking your home center... Since 220v tools draw less current, approximately half, they can be less affected by an extra 10-20 feet of wire. ... I sometimes use the 20A 240V appliance/AC extension cords i find at my local Home Depot. They nicely fit my 20A 240V outlets, and aren't too long. They work fine with anything up to 3HP. Someday i'll get around to rewiring my machines with proper longer cords... Yeah, i don't like running circuits at anything near their max capacity, myself. A number of undesirable things start happening up that level. Wires heat/expand/contract more and can eventually start working loose from their connections, which can cause shorts and fires. Any imperfections/nicks/etc in the wires/circuits start becoming more of a factor. And of course if i've wired the circuit myself, there's bound to be some imperfections in it. So i like having a safety margin. Quote