Minor hiccup getting my new JJP-12 up and running

Featured Replies

I've finally gotten the shop to the point where I'm ready to connect my new Jet 12" jointer/planer and start making shavings. And ran into a hitch immediately. My electrician talked me out of getting 30amp outlets on the 220v circuit I had her install, going for a 20 amp circuit instead. I thought that 220v motors used less amps so didn't see the problems with that. However the Jet 12" jointer/planer calls for a 30 amp circuit. Not sure if they are being really conservative because the motor is rated 3hp at 13 amps. Why is it calling for a 30 amp circuit? Bigger draw on startup?

I verified that she did use 10/3 wire to run to the outlets, so to my limited electrical knowledge it should be as simple as swapping out the outlets and breaker and getting the appropriate plug for the Jet? Also the power cord is 14awg, which seems really undersize for something that's requiring a circuit that code calls for 10awg wiring in the wall. And it's too short for where I want to run the tool, towards the center of the shop, so I want to swap it out for a 25' cord, or rig an extension cord for it.

I was set to go at home depot, with all the stuff in my cart and realized that I was exceeding my comfort level. Are there any gotchas that I don't know about? Should I pay an electrician to do the swap for peace of mind, to keep from burning the shop down? Would the existing 20 amp circuit be fine?

I can also swap my Jet 12" bandsaw over to 220v, not sure what the advantage to doing so would be though? Would be easy enough to do at the same time if that gains me something.

I've done some of this stuff. should be pretty easy, like you said, to switch it over to a 30amp. However, I feel much more comfortable having someone that is licensed to do it for a living do it. And they can convert your BS at the same time.

good luck. wish i had a 12" jointer I was trying to set up...

If she ran 10-3 wire to the circuit all you have to do is replace the breaker for a 30amp, turn off the main breaker, and the panel is dead now all you need is a screw driver pop the old breaker out they usually just rock out of bus bars there will be two wires one white, and one black unscrew the set screws pull the wires out than pug the wires into the new breaker it doesn't make any difference which wire plugs in where pop the new breaker back into the bus bars replace the panel cover, and turn the main breaker back on, now you're golden.

It doesn't make any difference which wire plugs in where...

White is neutral, black (or red or blue) is hot. Green or bare copper is ground.

I had a ceiling light fixture that wouldn't turn off. No one could figure out why. Then one night a buzzing sound woke me up, and I followed the sound to the light fixture. Smoke was coming out of it. If it hadn't also been buzzing (alternating current causing an intermittent arc) I probably would have slept until the smoke detectors went off. It turns out that someone had switched hot and neutral, so the light switch was on the neutral line, and when it was turned off the circuit was broken, but the hot line was still hot at the fixture. When the hot (now neutral) line shorted to ground, instead of popping the circuit breaker it completed the circuit and the light stayed on when the switch was off.

The main problem was the short to ground, but if hot and neutral hadn't been reversed, it would have been much easier to find the problem and repair it.

The line to your outlet should have three wires: the ground (bare or green) goes to the ground bus, the neutral (white) goes to the neutral bus, and the hot (black or some other color) goes to the circuit breaker. Unless it's a GFI breaker, in which case it need to be connected to all three wires so it can detect ground faults.

At least, that's my understanding. I'm not an electrician.

On a 220 circuit you have two power legs(the white/black wires I was talking about) each leg is 110 v add the two legs 110v +110v you have 220 v the ground doubles as the neutral I'm not a electrician either but being in construction most of my life I study how all the different trades do things, and ask as many questions as possible I've wired my own house,and shop I passed all of the electrical inspections if I have a question I have two good buddies that are electicians to ask. And I called them all the way through my construction prossess whenever I needed info on codes, or wire recomendations for electric stove/oven drier ect. I also had them inspect my work before I called for an inspection. Replaceing the breaker in the panel is a pretty easy operation as long as you turn off the main breaker. If you take the cover off your breaker panel the grounding bus bar holds all your ground wires it also holds the neutral wires all the hot wires conect to the breaker switches 220v circuits don,t useually have GFI's unless you are hooking up a hot tub or swimming pool, or anything that is around water power tool circuits aren't required to be GFI. If you have a red, black, white, and ground the hot legs would be the red, and black the white would be the neutral and would hook into the gounding bus bar along with the ground wire. But if your uncomfortable working with electricity I would call a electrician.

==> If she ran 10-3 wire to the circuit all you have to do is replace the breaker for a 30amp,

+1

The reason Jet wants 30a is startup surge. The circuit will probably draw less then 20a in normal operation. One more thought, did you check on the actual wire that's it's 10/3 or just call the electrician...

One other thing... Usually, a licensed electrician would run 12/3 for 20a unless the distances are long (or you mentioned that you may look at 30a in the future and just want to pay for the wire once). If the total distance from breaker to tool is greater then about 100', then you need to up a gauge.

They do make breakers that are designed to handle start up surge but not a constant overload. That might solve the problem without changing everything else. I remember them being called "slow blow" or something like that.

Modern non-GCFI/AFCI/etc breakers are 'slow blow' to account for reasonable surge... Making some assumptions about the motor, 3HP under load would draw about 16 or so amps. Using same assumptions gives an inrush of about 29a (hence the desire for 30a circuit). However, the inrush is [usually] within the time delay of the breaker so under normal circumstances a 20a should be fine (assuming it's a good quality breaker)... With the over-inflated HP specs these days, I doubt that the 3HP rating is real (probably more like 2.5HP), so the power requirements are also backed-off.

With usual legal caveats about qualified electrician aside, if this were my shop, I'd use the 20a and see if it ever trips -- it probably won't. I say this because [almost] all my stationary tools are 5HP or 6.5HP and the manual recommends 50a or 60a circuits to account for inrush. However, I put them on 30a/40a because that's what the full load requires and have never had a breaker trip in 10 years.

I agree with most of what has been said. I was an electrician in a previous life. Check for # 10 wire, replace the breaker, replace the outlet and replace the power cord with #12 wire. And yes it OSA the locked rotor current that causes the need for larger breaker. Very high current on startup and then normal once the motor starts to spin.

BRuce

  • Author

I'm 99% sure it's 10/3, I took pictures before the Sheetrock was installed and the 220v runs are orange insulated, the 110v runs are yellow insulated 12/3.

Thanks for the feedback folks. Don't think I'll run the tool on the 20amp circuit. The only question if I will do the work or hire an electrician.

  • 5 weeks later...
  • Author

I had an electrician come over and fix the wiring.

I ended up having him replace the breaker, fabricate an extension cord appropriate for the amperage, and replace the outlets with 30amp ones. I also had him break out the 220v outlets onto two breakers in case I wanted to ability to run two 220v tools at the same time in the future.

I'm glad I went this route as he found a couple of things that while not dangerous, weren't done to best practices. It cost me the $200 in parts and three hours labor, but peace of mind came with that.

And that 3hp motor sounds beautiful firing up. Can't wait to make sawdust with it. :)

Tex, let us know how you make out with your combo machine. I really love my Grizzly with the spiral cutter head.

chris

  • Author

I will, when I get a chance to use it. Had class today and tomorrow, this weekend will be the first chance I'll get to do so.

  • 3 weeks later...
  • Author

Jeez I love this jointer.  I've been using it for a wooden plane class to prepare the mahogany blank.  It was set up out of the box and required zero adjustment.  Jointing the blank was easy, and switch over to planer mode is very quick.  I love that I can leave the fence set and locked while swapping over, so I don't have to set that up every time I switch over.  

 

I used it to sneak up on a fit on the two 7/16" cheeks with zero problems, and zero tearout.  I'm loving my big boy jointer. :)

Awesome dude!!!  Glad you're enjoying the combo.  It's so darn nice to be able joint up to 12".  They run like butta!  B)

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Forum Statistics

  • Total Topics 32.1k
  • Total Posts 437.6k

Member Statistics

  • 26,011 Total Members
  • 3,644 Most Online
  • bobtjanitor Newest Member ·

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.