Electrical Advice

Featured Replies

I'm looking to upgrade my planer and jointer.  I may go as far as a combination set, which leads to my question about power.

I currently have one (count 'em) 220V outlet in my shop, normally running the table saw.  I believe it's on a 12 gauge wire.  There's a 20 Amp breaker on it.

I'm guessing at the wire size based on the measurement of the (bare) ground wire.I'm assuming the ground is the same size as the conductor.  If I'm off, I may have a 10 gauge wire.

Now, the "easy" answer in determining wire size is to pull the outlet and check the wire.  Tried that.  The problem is that the electrician left zero slack, and I can't read the writing on the insulation.  That's why I measured the ground wire.

If I go with a combination planer/jointer, I will need a 30 amp circuit.  Before I go and "upgrade" the breaker in the box, I want to make sure the wire can handle it.  Distance from the box to the outlet (along the wire) is about 30 feet.  My feeble understanding of NEC is that I need 10 gauge for a 30 amp circuit.  Is there another way to confirm size?

 

I am on the fence on getting either a 12 inch combo machine or an 8 in jointer with a 15 in planer.  Combo has the advantage of taking up less room.  I loose on planer size but gain on jointer size.  Changeover time/effort does not concern me.  With my current small shop, I spend just as much time wheeling one machine out of the way and wheeling in another, and then changing the dust collection hose as I would flipping tables and moving the collector.  It would probably actually be easier.  Additional advantage of the two machines is my 20 amp circuit is just fine.  So if the wire size is smaller, I can go the easy route.  But if it can handle a bigger breaker, it may be worth the effort.

 

One idea... Pull the panel cover and check the markings on the insulation at the branch...

If the wiring is original, the odds are overwhelming that it's a 12/2+g on a 20a branch...

Gauging the ground was a good notion, but unfortunately, sometimes the gauge of the ground isn't the same as the conductors... Sorry...

 

Yup, should be easy to check at the panel so long as it's romex and not stranded. White = 15amp Yellow = 20amp Orange = 30amp.

Only if the wiring was done reasonably recently (I think last 10-15 years?  Trip will know).  My wiring is 20 years old and predates the common color coding - all the romex in my house is white (other than wiring I've done recently myself).

Still, the suggestion to check the panel is a good one.  You should be able to read the romex there even if it's all white.

==>White = 15amp Yellow = 20amp Orange = 30amp.

Colors are a 'quick check' only... For safety/code, you should always check the gauges stamped on the insulation...

Why? Color coding was introduced by Romex around '00 and believe it remains common practice, not code... You can, in fact, get Romex in just about any color you want. While the overwhelming practice will use the common colors as intended, you can get fooled -- think 'left over' supplies from a previous job where colors were used to indicate type of branch, not gauge...

Trip offers some sound advice. Pull the break box panel and check the wires going to the breaker (Turn off the breaker for good measure.) There are also wire gauge tools like this to measure the wire gauge.

 

s-l1000.jpg

==>Turn off the breaker for good measure

While not standing in a puddle of water --- in bare feet... :)

Yup, should be easy to check at the panel so long as it's romex and not stranded. White = 15amp Yellow = 20amp Orange = 30amp.

Depends on how old it is.  They didn't start color coding the wires for inspectors That long ago.  It used to be all white.

I'd just run another circuit so you don't have to plug and unplug to use anything.

Edited by Tom King

Depends on how old it is.  They didn't start color coding the wires for inspectors That long ago.  It used to be all white.

Gotcha, I did realize this. This advise was to point him in the right direction. Most were cloth and not plastic coatings back then. If you see yellow you can obviously assume it's rated for 20amp though. If you look at the sheathing it will confirm that.

Edited by Janello

==>Depends on how old it is.  They didn't start color coding the wires for inspectors That long ago.  It used to be all white.

 

==>Most were cloth and not plastic coatings back then

 

Cloth was common in residential construction prior to about 1950 (this was also the era of two conductor without ground wiring). As a side note, I have a home that was full of the stuff... Colored Romex was commonly available starting '00-'02, and adopted over time. US/Canadian homes built between 1951 through 2001 will be white thermoplastic Romex. After that, most (not all) will be color-coded Romex. Color-coding for gauge is common practice in current residential construction, but not code. As another side note, the home with the cloth two-conductor wiring was retrofitted with a new service and all current wiring in '10 -- the electrician used all white Romex.

Edited by hhh

Hate to be the one to say it, but get a licensed electrician to do the work. Better safe than sorry  

yep, get a pro, and while he's there have him run wire for more outlets, can never have enough in a shop

Gotcha, I did realize this. This advise was to point him in the right direction. Most were cloth and not plastic coatings back then. If you see yellow you can obviously assume it's rated for 20amp though. If you look at the sheathing it will confirm that.

Not at all. I have used rolls of yellow 14 rated for 15 max. 

  • Author

Thanks guys, that's very helpful.  The house certainly isn't that old, and the yellow insulation leads me to believe that 12 gauge is most likely.  Not smart to just throw a 30 amp breaker on it.  This is making me lean towards the stand alone machines, which, long term, is probably the better answer.  Now, to decide on spiral cutter head, or standard.  Decisions, decisions...

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Forum Statistics

  • Total Topics 32.1k
  • Total Posts 437.6k

Member Statistics

  • 26,009 Total Members
  • 3,644 Most Online
  • Joseph b Newest Member ·

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.