Shop wiring

Featured Replies

I'm getting close to doing some extra wiring in my shop build. My portion of the building is 22'x30' of an existing 30'x50' metal building. It was already nicely wired with a good amount of 110v outlets on 20 amp breakers and 1 dedicated 220v outlet on a 50 amp breaker for a welder. 

My plan is to run a new 110v circuit for lighting a dedicated 220v 30 amp circuit for future AC/heater mini heat pump and a 220v 30 amp circuit with 3 outlets (stubbed down through the ceiling) for 220v tools (I'm a one man show so only 1 big tool at a time will be running on this circuit). I don't really weld much so I'm thinking of coming off of the 50 amp circuit and dropping it down with a sub box to 30 amp for DC. All of this will be run in conduit. 3/4 for the 220v circuits and 1/2 for the new 110v circuit. 

Any electrical gurus here with better suggestions I'm open to them. 

Also not decided on lighting type but leaning toward LED. 

I'll post a photo when I've made a bit more progress  

Thanks

Mike T

 

 

Mike, no where near an electrical guru, in fact, turning on a flashlight scares the heck out of me. I'm sure others will chime in. Good luck on your new shop. 

11 hours ago, Mike T said:

...a dedicated 220v 30 amp circuit for future AC/heater mini heat pump and a 220v 30 amp circuit with 3 outlets (stubbed down through the ceiling) for 220v tools...

All of this will be run in conduit. 3/4 for the 220v circuits and 1/2 for the new 110v circuit.

Why 3/4 for the 220V?   What size wire?   Unless you have long runs or some other condition, you only need 10ga for 30A which works in 1/2 conduit (up to 5 10ga wires in a 1/2 EMT).  You might also check any applicable codes in your area because I think 30A may be a cutoff for when it needs to be a dedicated circuit, so you might not be strictly allowed to have multiple outlets on it.

  • Author

The reason for 3/4 conduit at least on one run is that I also plan on having 110v wire in those same outlets. 

You want two 240V circuits, one for dust collector and one for tool. Add a third for your heat pump. When I wired my previous shop I did each 240V outlet on its own circuit because I moved things around a lot. You can just keep the 50amp wired up if it's a good spot for a DC otherwise just replace the outlet and breaker down to 20 or 30 amp.

Since the breakers can be cheap it was little extra cost to put each 240V outlet on its own circuit. I also hate wire nuts and splicing in boxes so that was also nice with complete runs all to the panel.

Just watch the fill capacities on the conduit, while it may be permissible to cram a lot of wires in it may not be possible to pull them.

Yes, you can get a lot of wires in a 3/4" conduit, up to 16 #12 T90, or 9 #12 & 4 #10 wires. There are derating factors to apply with increased fill though.

  • Author

Thanks guys. Sounds like we're pretty much on the same page. Looking forward to getting this stuff done so I can start to collect things to plug in. 

Regards

Mike T

  • Author
7 hours ago, wtnhighlander said:

Mike, the LED lighting available today is great stuff. Don't buy the cheapest, but it isn't critical to buy the most expensive, either. I prefer lights with 5000k color temp, and a color rendering index above 80.

Ok now the lighting experts. The space is approx 22'6" x 30' with 10' ceilings. How many fixtures to do a good job of lighting and can whatever that number is be run on a single 20 amp circuit?

My shop is about 22' x 23'. I have 4 rows of 4', 2 lamp fluorescent fixtures with 4 fixtures in each row for a total of 32 lamps. The light in there is very good. The lamps are Philips TL950, which are 5000 K with a CRI of 97.

If you put 6 rows in your shop, it would be equivalent. They would run on a 20A circuit

I love LED lighting & install tons of it, but for top quality light, fluorescent is still the best value. If you're willing to go with lower CRI of say 80, then LED makes sense.

Do not be tempted by the siren song of cheap LEDs though. Terrible CRI, high failure rate, & LEDs that are at half brightness after only 10,000 hours. If you want good LEDs, check out Big Ass garage lights. Expensive, but reportedly very good. 

'Good lighting' is highly subjective. Many lighting manufacturers have calculators on their web sites to help you out.

I will say that IMO, color temp and CRI make more difference that straight lumen output. Comparing HPS high-bays at work to LEDs in the 4500k range or above, the LED provides much better visibility at just 10% of the lumens.

4 hours ago, Mike T said:

The reason for 3/4 conduit at least on one run is that I also plan on having 110v wire in those same outlets. 

Putting another circuit in that same conduit is going to guarantee derating so you'll have to run bigger wire...hardly seems worth it.

Correction Edit:  I guess this is not technically true...as long as you keep it to 6 conductors or less in there, the 80% derated value of 10ga will still be good for 30A.

Edited by Vyrolan

1 hour ago, Mike T said:

Ok now the lighting experts. The space is approx 22'6" x 30' with 10' ceilings. How many fixtures to do a good job of lighting and can whatever that number is be run on a single 20 amp circuit?

Vic is the man to talk to about lighting.  PM him, as I have not heard from him on a while on the board.

  • Author

This might qualify as a big ass garage light. These are gas lights and I had 3 of them in this 50' space centered down the middle. To large a fixture hanging from a 10' ceiling and I'm betting they are cheap. This one wasn't working when I took it down. Haven't had time other than checking the bulb to see what's wrong with it. 

5 hours ago, Mike T said:

This might qualify as a big ass garage light. These are gas lights and I had 3 of them in this 50' space centered down the middle. To large a fixture hanging from a 10' ceiling and I'm betting they are cheap. This one wasn't working when I took it down. Haven't had time other than checking the bulb to see what's wrong with it. 

Problem with those is that they're not much good below about 15'. There's just so much light from them that glare is a problem.

These are the lights I was referring too:

header_image.jpg

  • Author

Wow those are pricey. Unless I'm reading it wrong. $400 a piece?

Yes, very pricey. I certainly can find better ways to spend my cash.

Well, it depends a lot on your budget, but I found some very decent lumen-per-watt-per-dollar callibrated 5500k bulbs for my work area. Based on the size, I estimated I'd need 4 of the 35w lights at least to have a reasonable "indirect sunlight" type of lighting.

My previous lighting prevented me from doing any type of detail work after 4pm, those were 3x 30W CFL bulbs. I bought and installed 1 of the new 35w LED bulbs and it really was a WOW moment for me, what a difference it made. It still doesn't allow me to cover the whole place with light, but it certainly is workable. And cheap. I'll purchase the other 3 very soon.

The lights are Neewer 5500k, you can find them on Amazon in 25, 35 and 45w versions, although the 45 is said to have a rather loud fan, which I wouldn't trust to have a long life.

Here's a reference document for light levels I found useful https://goo.gl/RYtDt0

 

Hope this helps.

  • 4 months later...

Hi Mike, Not sure I'd call myself a guru, but I have learned a lot in doing the electrical work on our addition and in my previous shop.

First of all, good idea having a dedicated circuit for lighting. Personally, it bugs me when something with a motor starts up and the lights dim. Since you're using conduit, I'm assuming you're using individual THHN or THWN wires, and not NM type cable, is that right? Also assuming you're using conduit to protect the wires because the walls won't be closed in? If they are going to be inside a wall, I won't harp on NM cable (romex) instead of conduit, other than to say there's a tradeoff there in time to cut, bend, and secure the conduit. Not to mention additional cost.

I wonder whether 30A capacity on a 240V circuit is really needed. When tools run on 240V, the current draw goes way down, and I question how many WW tools are going to pull more than 20 amps at 240V (I bet most will be < 10A).

Someone else maybe mentioned this too, but to use the welder circuit for smaller tools, you don't really need a subpanel, just change the breaker to 30A or 20A or whatever max capacity of the receptacles that you're going to put on that circuit. 8ga cable on a 30A ckt is overkill, but acceptable.

You said something about 110V wire in the same "outlets"... do you mean 220V and 110V receptacles in the same box, so you'll have different size wires in the conduit for both? (10ga for the 30A/220V, and 14ga for the 15A/115V?)  Here's where things could be simpler if you didn't need the 30A. Run a 3-wire 12ga setup, and then you could wire both your 220V and 115V receptacles from that same circuit. I really like the flexibility this gives. My new shop has three 20A receptacle circuits with 3-wire cable, so at any time in the future I can replace a 120V receptacle with a 240V recep just by changing the wires already at that box.

Probably could go on, because this is all fresh in my mind, but the only other thing I'd mention is watch your box fill. I bought a boatload of 12.5 cu in boxes thinking I'd need them in a lot of places, and then when I got around to checking box fill, realized that they were too small for anything except a single switch or receptacle and a single cable coming in! :wacko:
Of course this depends on your inspector, too. They may not bother to check this, but could be a pain if they flag boxes that are too small.

Anyway, good luck!

Keith

As someone said above, "lighting is subjective".  My preference for shop lighting is 4000K, I find it to be more of a neutral color.  I think the 5000k stuff has too much blue in it.

For the last year or so I've been installing 4000K LED shop lights from Home Depot; I just tried to find them online but came up short.  But they're on display in the shop lighting section if you want to check them out in real life.  

I'd suggest when you wire up your lights to use 2 or more switches.  In my shop I have one switch for the workbench area, where I spend most of my time, and another for the rest of the shop.  

Good luck!

Rich

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

Forum Statistics

  • Total Topics 32.1k
  • Total Posts 437.6k

Member Statistics

  • 26,009 Total Members
  • 3,644 Most Online
  • Joseph b Newest Member ·

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.